30 amp or 50 amp

I recently pulled into a site and the 30 amp plug had an open ground. I have a 30 amp rig. The host could not get maintenance until the next day. I checked the 50 amp and found it to be fine so plugged into 50 amp and used it. The next day the electrician? Came and changed out the 30 amp plug and problem solved. He recommended that I always use the 50 amp outlet when available. I know the main 30 amp breaker in the motorhome should protect the electronics, etc. The question to those electric minded individuals. Is it a good general practice to use the 50 amp circuit with an adapter to run my 30 amp coach? I don't have a fancy electric monitor system (on the wish list) just a cheap surge protector. Thanks in advance for your advice.

__________________
JamJanTan is offline   Reply With Quote
Old 09-23-2017, 04:45 PM   #2
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
I like to keep things simple: plug into, and use what your rig wants... (30 amps for your case...)
But that's just me I do this because I'm as ignorant about 'lectricity; as Hogs are about the Sabbath!
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 09-23-2017, 05:12 PM   #3
Senior Member
 
Brand: Still Looking
State: Tennessee
Posts: 297
THOR #7227
Quote:
Originally Posted by Bob Denman View Post
I like to keep things simple: plug into, and use what your rig wants... (30 amps for your case...)
But that's just me I do this because I'm as ignorant about 'lectricity; as Hogs are about the Sabbath!


I'm bout lik u on the legtricity
__________________
JamJanTan is offline   Reply With Quote
Old 09-23-2017, 05:25 PM   #4
Senior Member
 
Brand: Thor Motor Coach
Model: Windsport 29M
State: New York
Posts: 148
THOR #8264
I'm not an expert either, but logic would tell me you just have more current available to draw from with 50amp service. Your breaker panel will only allow you to use so much. My home breaker panel is 200 amps but I'm sure what is coming from the street is much higher.
__________________
PNTR10 is offline   Reply With Quote
Old 09-23-2017, 05:49 PM   #5
Senior Member
 
Brand: Still Looking
State: Tennessee
Posts: 297
THOR #7227
Quote:
Originally Posted by PNTR10 View Post
I'm not an expert either, but logic would tell me you just have more current available to draw from with 50amp service. Your breaker panel will only allow you to use so much. My home breaker panel is 200 amps but I'm sure what is coming from the street is much higher.


Agreed I think that was the logic the guy who changed the plug stated. Also said the parks he covers has much less problems with the 50 amp circuits one reason is they receive less usage than the 30 amps. Stated he works on 30 amp circuits about 4 times more often than 50 amps. Just musing but thanks for your input.
__________________
JamJanTan is offline   Reply With Quote
Old 09-23-2017, 05:49 PM   #6
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Technically the 30-Amp cord and motorhome wiring to the breaker panel isn't protected at 30 Amps like it should be, but in practice I'm not sure there is a significant risk since the 30-Amp breaker will limit current draw to well below 50 Amps anyway.

If for some reason the 30-Amp cord grounded, it would likely trip the 50-Amp breaker pretty fast, so distinction between 30 and 50 Amps isn't that important in my opinion.

I suppose that if a knucklehead connected their 30-Amp cord to 50-Amp at pedestal, and then used another adaptor to split power at motorhome to power 30-Amp motorhome and something else (like a second A/C or an electric skillet), then it would be possible to overload the 30-Amp cord and cause damage.

It's for that reason that the code (as I recall) requires breakers to be sized to protect what's immediately downstream -- in this case 30-Amps and not 50-Amps.

Personally, I'd stick to plugging into 30-Amp breaker unless your adaptor has a built-in 30-Amp breaker.
__________________
Chance is offline   Reply With Quote
Old 09-23-2017, 05:52 PM   #7
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,046
THOR #7035
I agree with the maintenance guy for 1 reason: The 30 Amp breaker on a lot of poles has been used and abused for years and is likely been tripped many times, making it more likely to trip under 30 Amps. Use the 50 Amp and trust your input 30 Amp breakers as a "known" entity.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 09-23-2017, 05:57 PM   #8
Senior Member
 
bruno1950's Avatar
 
Brand: Thor Motor Coach
Model: A.C.E. 30.2
State: Ohio
Posts: 103
THOR #8054
I have a 50 amp outlet at my home because my original coach was 50 amp . My current ( no pun intended) coach is 30 amp. I have it plugged in all the time with no problem.
__________________
bruno1950 is offline   Reply With Quote
Old 09-23-2017, 06:28 PM   #9
Axis/Vegas Enthusiast
 
Brand: Thor Motor Coach
Model: Axis 24.4
State: Michigan
Posts: 9,837
THOR #1150
Not really an issue: Use either one. As mentioned above the breakers inside the coach will trip before the breakers on the pedestal. That is a good point, however, about the 30A plug getting a lot more use than the 50A one. Still, though, if the plug fits in pretty snug it is more than likely ok.

Personally we plug in the RV in the 30A plug, and the car in the 50A plug
Click image for larger version

Name:	DSC_0454s.jpg
Views:	324
Size:	232.7 KB
ID:	7081
__________________
2022 Thor Axis 24.4
2021 Mach-E
blog - https://spareelectrons.wordpress.com/
JamieGeek is offline   Reply With Quote
Old 09-25-2017, 04:59 AM   #10
Junior Member
 
State: Colorado
Posts: 6
THOR #7912
As long as your wire size is rated for the 50 amp service you can rely on your internal breakers the cord would need to be # 6 wire for the 50 amps and the 30 amp would need to be number 10 wire. Undersized wire could cause heat issues
__________________
rspicy is offline   Reply With Quote
Old 09-25-2017, 11:07 AM   #11
gmc
Senior Member
 
gmc's Avatar
 
Brand: Thor Motor Coach
Model: Hurricane 32A
State: Florida
Posts: 1,873
THOR #2829
Let's be realistic about the risk...
Talking about plugging a 30A cord protected at the far end by a 30A breaker into a 50A outlet.... To have a problem, there would need to be a failure in the cord, receptacle on RV, or transfer switch that would cause it to draw more than 30A and less than 50A..
Everything else in the RV is protected by the RV's 30A breaker.
The risk should be minimal.

I would think it is quite common practice to plug in devices less than the rated circuit... Do you ever plug a 15A cord into a 20A circuit at home?
This would have less protection than what we are talking about here since there is no protection downstream of the 20A breaker.

NEC even allows multiple 15A recepticles to be on a 20A circuit... (The hard wiring must be rated for 20A, and if a SINGLE recepticles then it must be 20A. The 'pass thru' on 15A outlets is rated at 20A.). It's left to the user not to attempt to draw 20A through a single 15A recepticle.

You can decide for yourself what the risk is. Personally I wouldn't hesitate to do so.
__________________
Greg
Not yet retired...
Florida (Michigan transplant)
2014 Hurricane 32A
2000 Infinity (previous)
gmc is offline   Reply With Quote
Old 09-25-2017, 11:50 AM   #12
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Quote:
Originally Posted by gmc View Post

.....cut....

I would think it is quite common practice to plug in devices less than the rated circuit... Do you ever plug a 15A cord into a 20A circuit at home?
This would have less protection than what we are talking about here since there is no protection downstream of the 20A breaker.

.....cut.....
Of course it's done on a regular basis. For example, the cord on some lamps with a 60-watt bulb isn't necessarily rated at 15 or 20 Amps. Since the bulb will limit power draw to less than 1 Amp, everything should be fine.

The bigger problem (and more likely) is when a homeowner plugs a 10-Amp rated extension cord into a 15 or 20 Amp circuit and then plugs in 15 Amps worth of Christmas lights without knowing he's exceeded the rating of the cord. That can lead to fires.

On a practical basis I agree with you that the risk is minimal, with exception I mentioned above; an RV owner could split power at motorhome and thus overload 30-Amp cord. It's highly unlikely anyone would do that, but it would be similar to powering too many Christmas lights with an underrated extension cord.
__________________
Chance is offline   Reply With Quote
Old 09-25-2017, 12:35 PM   #13
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,046
THOR #7035
Quote:
Originally Posted by rspicy View Post
As long as your wire size is rated for the 50 amp service you can rely on your internal breakers the cord would need to be # 6 wire for the 50 amps and the 30 amp would need to be number 10 wire. Undersized wire could cause heat issues
????

Nobody with a 30 Amp RV has a 50 Amp cord, nor is there any reason to have one, the RV will not pull more than 30 Amps for very long before it's breaker trips. Breakers/interrupts are sized so that voltage is interrupted closest to the load.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 09-25-2017, 12:42 PM   #14
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
That makes a lot of sense; I agree!
Why would anyone want the bulk and un-handiness of a 50 amp cord; when they can only pull 30 amps?
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 09-25-2017, 01:43 PM   #15
Senior Member
 
Hooligan2's Avatar
 
Brand: Thor Motor Coach
Model: 2016 Siesta Sprinter 24ST
State: Florida
Posts: 602
THOR #2812
The 50 amp plug provides two- 50 amp circuits, using a 30 amp adapter you connect to one side of the plug, insuring you will have a full 30 amps available. Again your RV is not going to draw more than 30 amps without your circuit breaker opening. Using a 30 amp circuit, the most you will have is 30 amps, less losses from old or poor connections, line loss etc.
My unit shows voltage and amp demand on the surge protector display. Most connections show the same input voltage, but I have seen as much as 5 volts higher input from 50 amp adapter compared to 30 amp connection on same box.
FWIW When the voltage is higher, the display also shows the amp draw for the same load is lower
When available I use the 50 amp adapter with 30 amp power cord..
__________________
U.S. Coast Guard retired- 1956-1985
Pensacola, Florida
2016 Siesta 24ST
1972 Moto Guzzi Eldorado
Hooligan2 is offline   Reply With Quote
Old 09-25-2017, 01:49 PM   #16
Senior Member
 
Brand: Thor Motor Coach
State: Florida
Posts: 1,241
THOR #1249
Quote:
Originally Posted by Tfryman View Post
I agree with the maintenance guy for 1 reason: The 30 Amp breaker on a lot of poles has been used and abused for years and is likely been tripped many times, making it more likely to trip under 30 Amps. Use the 50 Amp and trust your input 30 Amp breakers as a "known" entity.
Right. If I am at an older, more neglected campground and the 30am breaker and female connection looks ratty, I will use the 50 amp if available with no problems.
I have used 30 amp connections where the plug got so hot you could hardly touch it due to worn out contact with the female connection.
__________________
Former owner of 2015 Thor Vegas 24.1 in Ocala
mcr1010 is offline   Reply With Quote
Old 09-25-2017, 02:09 PM   #17
gmc
Senior Member
 
gmc's Avatar
 
Brand: Thor Motor Coach
Model: Hurricane 32A
State: Florida
Posts: 1,873
THOR #2829
Quote:
Originally Posted by Hooligan2 View Post
...
Most connections show the same input voltage, but I have seen as much as 5 volts higher input from 50 amp adapter compared to 30 amp connection on same box.
FWIW When the voltage is higher, the display also shows the amp draw for the same load is lower
...
Absolutely... The math is always Watts = Volts * Amps...
The higher the volts, the lower the amps to deliver the same watts (power).
__________________
Greg
Not yet retired...
Florida (Michigan transplant)
2014 Hurricane 32A
2000 Infinity (previous)
gmc is offline   Reply With Quote
Old 09-26-2017, 12:16 AM   #18
Junior Member
 
State: Florida
Posts: 17
THOR #8840
Quote:
Originally Posted by JamJanTan View Post
I recently pulled into a site and the 30 amp plug had an open ground. I have a 30 amp rig. The host could not get maintenance until the next day. I checked the 50 amp and found it to be fine so plugged into 50 amp and used it. The next day the electrician? Came and changed out the 30 amp plug and problem solved. He recommended that I always use the 50 amp outlet when available. I know the main 30 amp breaker in the motorhome should protect the electronics, etc. The question to those electric minded individuals. Is it a good general practice to use the 50 amp circuit with an adapter to run my 30 amp coach? I don't have a fancy electric monitor system (on the wish list) just a cheap surge protector. Thanks in advance for your advice.
The simple answer is no. The cord will burn before the breaker will trip as the cord is only rated for 30amps....
__________________
Love2camp is offline   Reply With Quote
Old 09-26-2017, 12:28 AM   #19
Senior Member
 
Brand: Thor Motor Coach
Model: Windsport 29M
State: New York
Posts: 148
THOR #8264
Won't the demand only be for 30 amps? So your 30amp cord should be fine.
__________________
PNTR10 is offline   Reply With Quote
Old 09-26-2017, 12:31 AM   #20
Senior Member
 
Brand: Thor Motor Coach
Model: Gemini 24TX (Formerly)
State: California
Posts: 1,459
THOR #5821
I carry an adapter, so can plug into either, since the Gemini has only a 30 amp service. Even plugged into a 50 amp service, it still all goes through a 30 amp main on the motor home, so protection is still there.
__________________
Laco is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 09:17 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2