50 amp or 30 amp

Installing an electrical plug on side of house to plug RV into when parked. Occasionally I will have the need to run BOTH ac units. Is 30 amp sufficient?
__________________

__________________
Jim K - Avenue, Maryland
2016 Thor Hurricane 35C
2015 Ford F-150 King Ranch
2013 Chrysler 300 "S", 1936 Chrysler C-8
2012 Jeep Liberty Limited Edition
Brakeman48 is offline   Reply With Quote
Old 05-18-2018, 03:50 PM   #2
Senior Member
 
gnach's Avatar
 
Brand: Thor Motor Coach
Model: Axis 25.4
State: California
Posts: 494
THOR #6582
Quote:
Originally Posted by Brakeman48 View Post
Installing an electrical plug on side of house to plug RV into when parked. Occasionally I will have the need to run BOTH ac units. Is 30 amp sufficient?
Not for both, make it a 50a.
__________________

__________________
I'm wearing trifocals now but my hindsight is 20/20.
*************
Bilsteins and Sumos front and rear...HUGE! FatMat and Hoodliner...HUGE!
Hellwig sway bars F&R, 235/85 Hankook ATM, alignment...HUGE!!!
Battery watering, 260watts Solar and BigFeets to make life easier.
gnach is offline   Reply With Quote
Old 05-18-2018, 04:17 PM   #3
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
I agree... the cost difference is minimal, but the benefits are significant!
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-18-2018, 04:20 PM   #4
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Georgia
Posts: 3,243
THOR #11130
Also...study online the wiring of the 50A receptacle specific to RV's. It is different from a house circuit. Many have had a residential electrician install a 50A only to fry their entire RV with 220 the instant they plug it in. There is lots of info on YouTube on this. I'm no electrician but have read a few horror stories, so it's worth double checking.
__________________
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
The Gritz Carlton is offline   Reply With Quote
Old 05-18-2018, 04:43 PM   #5
Senior Member
 
TurnerFam's Avatar
 
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: North Carolina
Posts: 1,561
THOR #4735
actually, you can easily run two air conditioners on 30amps, just not much else. A 30amp outlet is much easier to add to your breaker box, as well.

there's also nothing to say that you can't also run an extension cord into the rv from a regular outlet at the house, for those 'other' item you might need at the same time.

50amp? sure, it's great, but for just parking next to your home... not needed, unless you think you'll be living in it one day : )
__________________
the Turners
'14 Palazzo 33.3 bunkhouse 34' diesel
KingTailgater2 Dish HD, 100w/5a SOLAR, BlueOx
93,000+mi since '14 - US, Alaska, Canada.... western NC for now : )
TurnerFam is offline   Reply With Quote
Old 05-18-2018, 04:47 PM   #6
Senior Member
 
gnach's Avatar
 
Brand: Thor Motor Coach
Model: Axis 25.4
State: California
Posts: 494
THOR #6582
Quote:
Originally Posted by gnach View Post
Not for both, make it a 50a.
Here's a good, up to date, primer on the wiring. It's about using the 4 wire 50A outlet and NOT the old 3 wire 50A stove outlet.
https://www.google.com/url?sa=t&sour...otTp7h0pdbW7Yh
__________________
I'm wearing trifocals now but my hindsight is 20/20.
*************
Bilsteins and Sumos front and rear...HUGE! FatMat and Hoodliner...HUGE!
Hellwig sway bars F&R, 235/85 Hankook ATM, alignment...HUGE!!!
Battery watering, 260watts Solar and BigFeets to make life easier.
gnach is offline   Reply With Quote
Old 05-18-2018, 05:26 PM   #7
Senior Member
 
saddlesore's Avatar
 
Brand: Still Looking
Model: SOB
State: Oregon
Posts: 561
THOR #3916
Quote:
Originally Posted by Brakeman48 View Post
Installing an electrical plug on side of house to plug RV into when parked. Occasionally I will have the need to run BOTH ac units. Is 30 amp sufficient?
It will be minimally sufficient..
IF you have 13.5k A/C units....
The cost of running a true 50a/30a/20a vs a 30a/20a is less than you think...For us the cost difference was less than $150 all in..
I had him replace/upgrade the House main breaker box, added two 50a/30a.20a RV outlet boxes (garage & RV pad)



..And I used a licensed & bonded Electrician, as we have way to much invested in our coach to take a chance of frying the electronics due to a half assed electrical installation.

AND the "biggie" is down the road you may upgrade to an RV that requires 50a with 15k A/C and Heat pumps... so just make it a "one and done" installation.
Attached Thumbnails
Click image for larger version

Name:	IMG_20180518_100747.jpg
Views:	149
Size:	130.5 KB
ID:	10317   Click image for larger version

Name:	IMG_20180518_100902.jpg
Views:	160
Size:	95.7 KB
ID:	10318  

Click image for larger version

Name:	IMG_20180329_151900.jpg
Views:	151
Size:	161.1 KB
ID:	10321  
__________________
current coach
SOB (some other brand)
former coach
Thor Infinity
saddlesore is offline   Reply With Quote
Old 05-18-2018, 06:06 PM   #8
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Georgia
Posts: 3,243
THOR #11130
If you're gonna do it at all...do it all the way.
__________________
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
The Gritz Carlton is offline   Reply With Quote
Old 05-20-2018, 07:38 AM   #9
Junior Member
 
State: Arkansas
Posts: 5
THOR #8577
50 amp 2 pole is 50 amp 2 pole. Should be fine. It's a 120/240 outlet for the 50 amp 2 pole outlet. It's the 30 amp single pole 120 outlet that people get confused on
__________________
iAmBlum is offline   Reply With Quote
Old 05-20-2018, 01:32 PM   #10
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
Quote:
Originally Posted by The Gritz Carlton View Post
If you're gonna do it at all...do it all the way.
I agree.
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-21-2018, 01:06 PM   #11
Junior Member
 
extex495's Avatar
 
Brand: Thor Motor Coach
Model: Four Winds [MB Sprinter]
State: Virginia
Posts: 7
THOR #11635
30a vs 50a

Something on 30a vs 50a that concerns me: if you were @ a hook up that was only 50a, and your coach is 30a, is the use of one of those 50a to 30a adapter plugs potentially harmful?? I have one, but the conservative [paranoid?] side of me has never let me use it....
__________________
FMCA #461433
extex495 is offline   Reply With Quote
Old 05-21-2018, 01:17 PM   #12
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
Relax... it's okay to use them!
Think of it this way:
50 amps worth of power isn't being shoved into your motorhome's electricals...
It only draws what it needs.
That 50 amp plug just means that more is available!
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-21-2018, 01:19 PM   #13
Senior Member
 
Brand: Thor Motor Coach
Model: Vegas 24.1
State: Florida
Posts: 401
THOR #5313
I hooked into a 30 AMP once that was wired like a 220v dryer. Luckily, only popped capacitors on convertor circuit board. I ended up ordering circuit board for convertor from Amazon and had it drop shipped. $145 plus an hour and a half troubleshooting and installing. Spent another 30 minutes correcting plug.

When I got home, I cancelled "Extended Warranty". $100 deductable and who knows how long waiting for repair? Local dealer closed location 30 minutes away and only has shop 2 hours away now. They did even give courtesy notice.
__________________
Muggs is offline   Reply With Quote
Old 05-21-2018, 02:19 PM   #14
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 3,755
THOR #2121
Itís ďALMOSTĒ always safe to use an adapter at pedestal, but not 100% of time because people are unpredictable. If done properly risk are very minimal, but the problem with circumventing preferred practices/rules is that the owner may not know much about electricity and could end up doing something stupid.

With one of these adapters a person could overload the 30-Amp power cable very easily if connected to 50-Amp service. Some owner may decide to run the RV from one branch, and then connect a second (stand-alone) air conditioner to other branch, or maybe an electric skillet that draws ~ 1500 watts (13 Amps), etc.

The point is that it is physically possible (however unlikely) to load 30-Amp cord up to 50-Amps before the pedestal breaker trips, or the 30-Amp cable overheats and starts a fire.

Safety rules are usually written to protect everyone, not just those with common sense.
Attached Thumbnails
Click image for larger version

Name:	38B0D2A7-70C4-4196-8AFC-612DE83D974B.jpeg
Views:	41
Size:	25.6 KB
ID:	10359  
__________________
Chance is offline   Reply With Quote
Old 05-21-2018, 02:22 PM   #15
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
Nice catch!

I forgot about our abilities to do foolish things...
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-21-2018, 02:30 PM   #16
Axis/Vegas Enthusiast
 
JamieGeek's Avatar
 
Brand: Thor Motor Coach
Model: Axis 24.1
State: Michigan
Posts: 7,869
THOR #1150
Quote:
Originally Posted by Bob Denman View Post
Nice catch!

I forgot about our abilities to do foolish things...
Again: The trouble with making something foolproof is that you always underestimate the fool.
__________________
2014 Thor Axis 24.1
2018 Chevy Bolt
blog - https://spareelectrons.wordpress.com/
JamieGeek is offline   Reply With Quote
Old 05-21-2018, 03:04 PM   #17
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
Quote:
Originally Posted by JamieGeek View Post
Again: The trouble with making something foolproof is that you always underestimate the fool.
Why is it that I keep seeing my own picture: above that phrase?
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-21-2018, 03:14 PM   #18
Senior Member
 
Brand: Thor Motor Coach
Model: 29h outlaw
State: New Jersey
Posts: 225
THOR #5248
Bob,
Your 29h is capable of running both air conditions on 30amp. That's the way it is designed. I do it all the time when the kids are using the garage as a bedroom. The back ac is only 5000btu.

I ran a 30 amp via conduit for mine. I figured if I ever upgrade to something with 50 amp I'll just pull anothe wire through the conduit.
__________________
Trkyte@msn.com is offline   Reply With Quote
Old 05-21-2018, 03:27 PM   #19
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
The Outlaw is set up for running them both on just 30 amps...

But one of them, is just a 5,000 BTU unit.
__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Old 05-21-2018, 05:12 PM   #20
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 9,491
THOR #8860
Back to that old saying for a moment...

http://www.thorforums.com/forums/att...1&d=1526922718
Attached Thumbnails
Click image for larger version

Name:	Foolproof.png
Views:	60
Size:	332.9 KB
ID:	10363  
__________________

__________________
Good Sam Member 843599689
FMCA Member F473304

Current coach: Tiffin Wayfarer 24 BW
Former coach: Thor Outlaw 29-H
Bob Denman is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 09:53 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2