Quote:
Originally Posted by RDC54
If you don't mind sharing, I would be curious to know what you figure out on this one. I think I have a similar thermostat in my 2018 Compass, but have not seen my display do what yours is doing (yet )
|
Well, if I'm reading it right, apparently it's
supposed to do what it's doing.
First of all, my model # is
331-2024 (without humidifier). It's also called a
CCC-2.
Next, I think this is the applicable section:
Auxiliary Heat (Heat Pump Models Only)
Auxiliary heat operation will be activated when the measured temperature of the outdoor
temperature sensor is less than 30º F. If the system is equipped with a furnace,
the control will select FURN heating mode for the auxiliary heat source. Auxiliary
heat operation, once initiated, will have priority over a heat pump defrost cycle.
Auxiliary heat operation will be de-activated and the heat pump operation will resume
when the temperature of the outdoor temperature sensor is higher than 35º F.
My thermostat display was alternating between
HP and
FURN when the temperature was below freezing. I think this indicates that I had set it to
HP, but it was overriding my setting in favor of
FURN. It went back to
HP after the temperature warmed up.
My only concern with this was that I think
FURN is using LPG, is it not? And I was low on LPG, so what happens if it runs out?