Quote:
Originally Posted by liz48@me.com
Having an electrical issue on 2015 Thor Tuscany 44MT on the GFI 15 amp circuits. There is only one reset/test outlet in the half bath which I replaced and then removed the replacement wiring direct.
The main bath outlet and the overhead sink outlet are working.
The outlets in bedroom under the tv and outside mounted on the cabinet are dead as well as the outlets in overhead compartment over driver seat and the outlet for the front TV.
Perhaps these outlets burned out as I heard a pop up front when I turned on the front TV.
I have talked to Thor Tech support at length, as well as, a Master Electrician that I know in San Antonio.
The Electrician believes that there must be a loose wire on the neutral side.
I show voltage and amperage at these outlets but they will not power the device that is plugged into the out.
|
With the big 44 foot buss, I can guaranty you have 2 or more GFI protection devices. If you heard a pop up front that is when I would start looking. Some have two GFI outlets in the bath. look around. Behind doors. sides of vanity's.
Basement storage areas also are GFI protected. Some coaches have a GFI breaker in the panel. It will have a yellow reset button on it.
I am a 45 year Master Electrician and do not understand "removed replacement wiring direct."
How did you measure amps with out voltage??
There is a GFI outlet on the inverter which probably controls the TV's. Hint hint.