Coach batteries not charging connected to shore Please Help
First, thank you for your help...
She is a Huricane 2006, class A
The batteries charger ( under the bed) is new.
The charger is providing 12v power, ( running from the generator or the shore)
test batteries light show 12v
amp test running the furnace indicate 14 amp provided by the charger DC clamp test
The coach batteries is engaged and the selenoid in the box under the hood is working fine. BCC
when switch is off, no 12v power in the RV. (no shore, no generator)
when switch is on, 12v power in RV (no shore, no generator)
everything is working on 12v (no shore, no generator)
But, the charger is not charging the coach batteries !
If I read the voltage at the coach batteries ( no shore, no generator) I have 12.1v, when I read the voltage at the coach batteries after starting the generator or plug the shore, Ie still see 12.1v, event 3 hours later.
In conclusion, batteries provide power to the coach, charger provide power to the coach, but the charger doesn't provide any power to the batteries!
Is there a fuses or something somewhere that will separate the charger power to reach the batteries?
This doesn't make sense to me!