Many 30 amp coaches run two air conditioners with no problem...but you're right. Beyond the two AC's you have too be frugal!
__________________

__________________
salzerj@comcast.net is offline   Reply With Quote
Old 09-23-2020, 11:09 PM   #62
Member
 
Bill Johnson's Avatar
 
Brand: Thor Motor Coach
Model: Thor Ace 33.1
State: Illinois
Posts: 45
THOR #20274
Quote:
Originally Posted by Chance View Post
Both inside and outside temperatures make a huge difference. See Coleman data below that ďapproximatesĒ effect outside temperature makes. Thereís other data for inside temperature. This isnít that accurate so donít take it as an exact correction.

Note also on 13,500 BTU/hour Power Saver data above that standard running Watts is 1,075 but that desert conditions is 1,320 Watts. Assuming same efficiency, power factor, and that voltage is reduced from 115 to 103.5 VAC per desert rating conditions, current would go from 10 Amps to over 13 Amps.
.
I just saw the same thing, so in my area 95 would be the high and that would be RLA let's say 13 amps at 80 degrees it would be about10 amps
__________________

__________________
Bill Johnson is offline   Reply With Quote
Old 09-24-2020, 09:15 AM   #63
Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 88
THOR #9178
Quote:
Originally Posted by Chance View Post
The best news is how much air conditioners have improved in efficiency, and that thereís still theoretical room for even more improvement.



A few years ago Coleman advertised how their 13,500 BTUH A/C reduced current from 15.3 to 11.2 Amps, and now they have specs showing 10 Amps. That 10 Amps is 1,075 Watts, which represents an EER of 12.5. Thereís definitely room to make that EER much higher and thus reduce electrical requirements below 10 Amps.



Even at 10 Amps, two units for a total of 20 Amps is quite below 30A service.





P.S. ó Iím a little skeptical about 10A rating and would want to see/measure myself, but even if close, itís pretty good.

.
My 1500 watt units draw 12 amps on high typically

Maybe an amp difference between the three at 120v per line

You can watch the amps climb when a camp ground has a high load
__________________
lwmcguir is offline   Reply With Quote
Old 09-24-2020, 09:27 AM   #64
Senior Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 876
THOR #6903
We have several large heat pumps at one home

The only correct to charge a 410a system is to use the sub cooling value for that particular compressor

Both outside and inside temperatures affect a compressor and condensr performance

You have to monitor the high side temp along with pressure to accurately charge

High temperatures do result in higher amp draw
__________________
lwmcguire is offline   Reply With Quote
Old 09-24-2020, 10:01 AM   #65
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 132
THOR #17765
Quote:
Originally Posted by Rcstroll View Post
Hi! Have 50 amp as well. Was able to use 2 a/c units on it and thought that i was doing great! I was... after 3 days of such use, broke camp and ...wow! The cables were super hot and the 50 to 30 cable burning hot!! Just pray I didn't do any damage. Never again... even if it works....
Yep. I melted a dogbone several years ago. Lucky nothing was damaged. So regardless of all the arithmetic calculations, Iíll stick to one AC and just sweat a little more in July in the Southeast.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-24-2020, 11:57 AM   #66
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 16,174
THOR #8860
That's why they invented "Sweet Tea" down South anyway...
__________________
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
"History shows again and again; how Nature points out the folly of Man!"
Bob Denman is offline   Reply With Quote
Old 09-24-2020, 12:55 PM   #67
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 4,688
THOR #2121
Quote:
Originally Posted by Jimbo56 View Post
Yep. I melted a dogbone several years ago. Lucky nothing was damaged. So regardless of all the arithmetic calculations, Iíll stick to one AC and just sweat a little more in July in the Southeast.

What do you think happened? You are not providing much information other that it involved 2 A/Cs. I donít know how else to say that all A/Cs are not the same and canít be treated as equals in ďcalculationsĒ.

Regardless, the obvious questions are that if you exceeded 30A, why didnít the breaker trip. And if you remained under 30A, then why did a 30A dogbone melt?

Proper electrical systems have protection so they remain safe even if owner overloads it. I wouldnít blame the math when something else went wrong. Besides, weíd still be in the Dark Ages if not for math and wouldnít be enjoying air conditioning at all.
__________________
Chance is offline   Reply With Quote
Old 09-24-2020, 12:58 PM   #68
Thor Palazzo 33.3 diesel
 
TurnerFam's Avatar
 
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,399
THOR #4735
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
__________________
the Turners
'14 Palazzo 33.3 bunkhouse 34' diesel
KingTailgater2 Dish HD, 100w/5a SOLAR, BlueOx
100,000+mi since '14 - US, Alaska, Canada - Hiawassee, GA! (also, '14 Gulfstream Amerilite and '07 ForestRiver Rockwood) : )
TurnerFam is offline   Reply With Quote
Old 09-24-2020, 01:23 PM   #69
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 5,025
THOR #7035
Quote:
Originally Posted by TurnerFam View Post
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
So do dirty/corroded connections - anything that causes the dogbone connection to have a higher than normal resistance will cause heat at that connection and the heat goes up exponentially as the current goes up.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad
2020 Chevy Colorado Z71 Trail Runner Alternate Toad
16ACE27 is offline   Reply With Quote
Old 09-24-2020, 09:51 PM   #70
Senior Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 876
THOR #6903
I don't think that there is anyone that has camped a number years that hasnít melted a couple of adapters and dog bones

Not trying to run e ac's necessarily either
__________________
lwmcguire is offline   Reply With Quote
Old 09-25-2020, 04:33 PM   #71
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 132
THOR #17765
I was in a 50 amp fifth wheel. One carrier AC. Using a 50 to 30 dogbone. A county park camp ground. Might have been a dirty connection. Maybe a loose wire in the pedestal. I donít know. I didnít try to diagnose it due to check out time. All I do know is that it was hot and gooey feeling when I turned the breaker off and went to pull it out of the plug. This coach is 30. Iíve done everything to make the one unit as efficient as possible. When in 98 degree high humidity with no shade, I can get it to 78. So Iím fine. Just sayin.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-25-2020, 04:38 PM   #72
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 132
THOR #17765
Quote:
Originally Posted by TurnerFam View Post
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
I was not trying to spread misinformation. Only responding to the guy who had a similar experience. I camp & travel for fun and enjoyment. Period.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-25-2020, 06:01 PM   #73
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 4,688
THOR #2121
For what itís worth (and we are all just sharing information in case it helps others in some way) the Forest River Sunseeker line of Class Cs is also offering dual high-efficiency air conditioners with 30A service. Along with Thor and others, itís now fairly common in what appears to be mid-size modest-cost motorhomes. Larger and higher-end gasoline rigs mostly continue to have 50A and 5,500 in lieu of 4,000-Watt generators that come with 30A electrical in these size motorhomes. The smaller generator should save both weight and cost.
.
Attached Thumbnails
Click image for larger version

Name:	5284EEA0-787B-4FFB-A787-2962C3DB58DE.jpg
Views:	3
Size:	62.1 KB
ID:	26308  
__________________

__________________
Chance is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 11:07 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2
×