Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 

Go Back   Thor Forums > Thor Tech Forums > Motorhome Tech Topics
Click Here to Login
Register FAQ Community Calendar Today's Posts Search Log in
Reply
 
Thread Tools Display Modes
 
Old 09-23-2020, 11:08 PM   #61
Junior Member
 
Brand: Jayco
State: New Jersey
Posts: 21
THOR #19560
Many 30 amp coaches run two air conditioners with no problem...but you're right. Beyond the two AC's you have too be frugal!

__________________
salzerj@comcast.net is offline   Reply With Quote
Old 09-23-2020, 11:09 PM   #62
Senior Member
 
Bill Johnson's Avatar
 
Brand: Thor Motor Coach
Model: Thor Ace 33.1
State: Illinois
Posts: 1,266
THOR #20274
Quote:
Originally Posted by Chance View Post
Both inside and outside temperatures make a huge difference. See Coleman data below that “approximates” effect outside temperature makes. There’s other data for inside temperature. This isn’t that accurate so don’t take it as an exact correction.

Note also on 13,500 BTU/hour Power Saver data above that standard running Watts is 1,075 but that desert conditions is 1,320 Watts. Assuming same efficiency, power factor, and that voltage is reduced from 115 to 103.5 VAC per desert rating conditions, current would go from 10 Amps to over 13 Amps.
.
I just saw the same thing, so in my area 95 would be the high and that would be RLA let's say 13 amps at 80 degrees it would be about10 amps
__________________
Bill Johnson is offline   Reply With Quote
Old 09-24-2020, 09:15 AM   #63
Senior Member
 
Brand: Thor Motor Coach
Model: Tuscany 42GX
State: Missouri
Posts: 1,158
THOR #9178
Quote:
Originally Posted by Chance View Post
The best news is how much air conditioners have improved in efficiency, and that there’s still theoretical room for even more improvement.



A few years ago Coleman advertised how their 13,500 BTUH A/C reduced current from 15.3 to 11.2 Amps, and now they have specs showing 10 Amps. That 10 Amps is 1,075 Watts, which represents an EER of 12.5. There’s definitely room to make that EER much higher and thus reduce electrical requirements below 10 Amps.



Even at 10 Amps, two units for a total of 20 Amps is quite below 30A service.





P.S. — I’m a little skeptical about 10A rating and would want to see/measure myself, but even if close, it’s pretty good.

.
My 1500 watt units draw 12 amps on high typically

Maybe an amp difference between the three at 120v per line

You can watch the amps climb when a camp ground has a high load
__________________
lwmcguir is offline   Reply With Quote
Old 09-24-2020, 09:27 AM   #64
Senior Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 2,326
THOR #6903
We have several large heat pumps at one home

The only correct to charge a 410a system is to use the sub cooling value for that particular compressor

Both outside and inside temperatures affect a compressor and condensr performance

You have to monitor the high side temp along with pressure to accurately charge

High temperatures do result in higher amp draw
__________________
lwmcguire is offline   Reply With Quote
Old 09-24-2020, 10:01 AM   #65
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 2,438
THOR #17765
Quote:
Originally Posted by Rcstroll View Post
Hi! Have 50 amp as well. Was able to use 2 a/c units on it and thought that i was doing great! I was... after 3 days of such use, broke camp and ...wow! The cables were super hot and the 50 to 30 cable burning hot!! Just pray I didn't do any damage. Never again... even if it works....
Yep. I melted a dogbone several years ago. Lucky nothing was damaged. So regardless of all the arithmetic calculations, I’ll stick to one AC and just sweat a little more in July in the Southeast.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-24-2020, 11:57 AM   #66
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
That's why they invented "Sweet Tea" down South anyway...
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 09-24-2020, 12:55 PM   #67
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Quote:
Originally Posted by Jimbo56 View Post
Yep. I melted a dogbone several years ago. Lucky nothing was damaged. So regardless of all the arithmetic calculations, I’ll stick to one AC and just sweat a little more in July in the Southeast.

What do you think happened? You are not providing much information other that it involved 2 A/Cs. I don’t know how else to say that all A/Cs are not the same and can’t be treated as equals in “calculations”.

Regardless, the obvious questions are that if you exceeded 30A, why didn’t the breaker trip. And if you remained under 30A, then why did a 30A dogbone melt?

Proper electrical systems have protection so they remain safe even if owner overloads it. I wouldn’t blame the math when something else went wrong. Besides, we’d still be in the Dark Ages if not for math and wouldn’t be enjoying air conditioning at all.
__________________
Chance is offline   Reply With Quote
Old 09-24-2020, 12:58 PM   #68
Senior Member
 
Brand: Thor Motor Coach
State: Georgia
Posts: 2,585
THOR #4735
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
__________________
the Turners...
two Campers, two Electric cars
former diesel pusher traveler
TurnerFam is offline   Reply With Quote
Old 09-24-2020, 01:23 PM   #69
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,329
THOR #7035
Quote:
Originally Posted by TurnerFam View Post
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
So do dirty/corroded connections - anything that causes the dogbone connection to have a higher than normal resistance will cause heat at that connection and the heat goes up exponentially as the current goes up.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 09-24-2020, 09:51 PM   #70
Senior Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 2,326
THOR #6903
I don't think that there is anyone that has camped a number years that hasn’t melted a couple of adapters and dog bones

Not trying to run e ac's necessarily either
__________________
lwmcguire is offline   Reply With Quote
Old 09-25-2020, 04:33 PM   #71
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 2,438
THOR #17765
I was in a 50 amp fifth wheel. One carrier AC. Using a 50 to 30 dogbone. A county park camp ground. Might have been a dirty connection. Maybe a loose wire in the pedestal. I don’t know. I didn’t try to diagnose it due to check out time. All I do know is that it was hot and gooey feeling when I turned the breaker off and went to pull it out of the plug. This coach is 30. I’ve done everything to make the one unit as efficient as possible. When in 98 degree high humidity with no shade, I can get it to 78. So I’m fine. Just sayin.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-25-2020, 04:38 PM   #72
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 2,438
THOR #17765
Quote:
Originally Posted by TurnerFam View Post
good question, CHANCE, as these are the types of 'stories' that easily lead to misinformation about how electricity 'works' - the owner does not understand that simply running two a/c units, or two of anything, has nothing to do with a 'melted' connector, etc. If a connection has an issue, it's with the wiring and connector, NOT the fact that the power was somehow 'overloaded' or anything - a loose neutral wire is a typical issue that cause overheating and melting within plastic housings, not the use of a/c units.
I was not trying to spread misinformation. Only responding to the guy who had a similar experience. I camp & travel for fun and enjoyment. Period.
__________________
Jimbo56 is offline   Reply With Quote
Old 09-25-2020, 06:01 PM   #73
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
For what it’s worth (and we are all just sharing information in case it helps others in some way) the Forest River Sunseeker line of Class Cs is also offering dual high-efficiency air conditioners with 30A service. Along with Thor and others, it’s now fairly common in what appears to be mid-size modest-cost motorhomes. Larger and higher-end gasoline rigs mostly continue to have 50A and 5,500 in lieu of 4,000-Watt generators that come with 30A electrical in these size motorhomes. The smaller generator should save both weight and cost.
.
Attached Thumbnails
Click image for larger version

Name:	5284EEA0-787B-4FFB-A787-2962C3DB58DE.jpg
Views:	46
Size:	62.1 KB
ID:	26308  
__________________
Chance is offline   Reply With Quote
Old 01-31-2021, 03:46 AM   #74
Member
 
Esqui's Avatar
 
Brand: Thor Motor Coach
Model: Vegas 27.7
State: Florida
Posts: 38
THOR #16050
Hello all,

So I'm in the process of buying a new 2021 Jayco Alante 29f and I have a question. The coach has two 11,000 BTU A/C units but a 30 amp service. Has anyone had a problem with this? Can anyone explain how Jayco is able to do this? I've always been of the mindset that two A/Cs required 50 amps.

Thank you in advance,

Esqui
__________________
Esqui is offline   Reply With Quote
Old 01-31-2021, 04:24 AM   #75
Senior Member
 
Brand: Thor Motor Coach
Model: Forest River Forester 235
State: Indiana
Posts: 4,884
THOR #6826
Quote:
Originally Posted by Esqui View Post
Hello all,

So I'm in the process of buying a new 2021 Jayco Alante 29f and I have a question. The coach has two 11,000 BTU A/C units but a 30 amp service. Has anyone had a problem with this? Can anyone explain how Jayco is able to do this? I've always been of the mindset that two A/Cs required 50 amps.

Thank you in advance,

Esqui


Well they’re smaller units and the energy management system certainly will help manage start up loads and maybe even sequence the start up or operation of the two units. Possibly they take turns actually cooling though I don’t think that would be very satisfactory for most people. In any event it probably is sort of marginal. Running your water heater on electric and using the microwave might be iffy. On the other hand you’ll probably only need both ACs during the heat of the day and you might well be able to manage your other demands accordingly. But all of that is a guess. Try before you buy!!
__________________
Pete'sMH is offline   Reply With Quote
Old 01-31-2021, 04:34 AM   #76
Senior Member
 
Down South's Avatar
 
Brand: Thor Motor Coach
Model: A.C.E 27.2
State: Louisiana
Posts: 242
THOR #17883
Quote:
Originally Posted by Pete'sMH View Post
Get one of these for about $10 and keep it plugged into a convenient outlet so you can keep an eye on park voltage. I’ve seen 107 during a hot day and 122 in the same park on the same day at night. I keep it in the bathroom and it’s just right for a night light as an added bonus. Autoformer is a bit pricey but is a useful addition to any coach.[ATTACH]26171
Thanks for the heads up. I have an EMS but I have to go outside and wait for it to cycle to volts to see what the current volts are at the time.
I can plug this little gem up inside the MH "Kitchen" and see my volts easily at a glance.
I ordered one from Amazon. They are $15 now.
__________________
2017 Thor ACE 27.2
Down South is offline   Reply With Quote
Old 01-31-2021, 04:35 AM   #77
Senior Member
 
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
Quote:
Originally Posted by mrgscooter View Post
Have a 50amp MH, thought could only a single ac unit on 30amps, first time at 30amp hookup and both work. I realize probably can't run much else with both units running however to just cool the MH on a hot day works great. Is this typical or is there anything special maybe on pedestal?
nope ANY RV should be able to run 2 A/C's with nothing else running.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 01-31-2021, 04:37 AM   #78
Senior Member
 
Down South's Avatar
 
Brand: Thor Motor Coach
Model: A.C.E 27.2
State: Louisiana
Posts: 242
THOR #17883
It doesn't take long to figure out that electric on the water heater + AC + Microwave = tripped breaker.
__________________
2017 Thor ACE 27.2
Down South is offline   Reply With Quote
Old 01-31-2021, 04:38 AM   #79
Senior Member
 
Brand: Thor Motor Coach
Model: XG 32 Omni
State: Missouri
Posts: 842
THOR #4243
I tried to run our 2020 Omni XG32 air conditioners on a 30 amp circuit just to see if it would do it, and it wont. Turned on the main coach a/c first waited a couple of minutes and turned on the a/c in the bedroom, and the system shut off the main coach a/c then turned on the bedroom a/c. so something in the touch pad controller or somewhere in the coach it will not allow to run both on 30 amps.
__________________
kwplot34 is offline   Reply With Quote
Old 01-31-2021, 05:09 AM   #80
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
NOT ALL AIR CONDITIONERS ARE THE SAME


The ones being questioned on Jayco are 11,000 BTU/hr Power Savers (energy efficient). They are rated under 11 Amps each under normal conditions if I recall correctly, so well under 30 Amps combined.

Standard 15,000 BTU/hr air conditioners can pull between 15 and 20 Amps each, so two CAN NOT run on 30A service. Details do matter.

Specs show MH comes with load shedding. One A/C should turn off under heavy loads, like when microwave is turned on. I’d confirm myself, and wait for A/C to come back on automatically after microwave shuts off. There may be a time delay, so give it time if A/C was off just for short period.
__________________
Chance is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.


Thor Motor Coach Forum - Crossroads RV Forum - Redwood RV Forum - Dutchmen Forum - Heartland RV Forum - Keystone RV Forum - Airstream Trailer Forum


All times are GMT. The time now is 09:08 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2