Quote:
Originally Posted by CSR View Post
We had an electrician look at the issue. He was convinced the problem is due the modified sine wave inverter. Something about the square wave pattern causing subtle faults that cause most GCFI receptacles to trip. Our dealer swapped the receptacle, but the problem continues to persist. We plan to upgrade to a pure sine inverter and see if we get better results.
That is what solved the problem for us.

__________________
m1noel is offline   Reply With Quote
Old 04-03-2018, 10:26 AM   #22
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Alabama
Posts: 11
THOR #11169
We bought a 2018 Aria 3901 in March. Same GFI issue but also popping cb#9. RV dealer has no idea what is on that CB. He says Thor has no schematic for their RV. Need to call Thor. GFI follows same pattern of changing power sources. Will show RV service this thread. Also having transmission issues. Luckily, that’s just a broken connector.
__________________
Markewelch is offline   Reply With Quote
Old 04-03-2018, 11:36 AM   #23
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Maine
Posts: 22
THOR #10229
Hi all, I mentioned this on another Aria post. The new GFI's do not like a modified sine wave inverter. You can not "test" a GFI on a modified sine wave inverter. You only test when on another power source. The reason a new GFI wouldn't work is because they "self test".

You have two choices.

1 fight with Thor and get a pure sine wave inverter.

2 go on EBay or Amazon and get an older model GFI Leviton 8899 and install it and the problem also goes away.

I am so mad at Thor I don't ever want to talk to them, so I went with option #2. We have been full timing for three months without a single trip. We have been in 11 different campground and gone back and forth between all power sources a lot. The model 8899 was an easy fix so we could get on with life.

Scott (Chesuncook 1)
__________________
Chesuncook1 is offline   Reply With Quote
Old 04-03-2018, 12:53 PM   #24
Senior Member
 
Brand: Thor Motor Coach
State: Georgia
Posts: 2,585
THOR #4735
Exclamation

Quote:
Originally Posted by Chesuncook1 View Post
You can not "test" a GFI on a modified sine wave inverter. You only test when on another power source. The reason a new GFI wouldn't work is because they "self test".

SORRY to disagree, but our GFCI outlets work perfectly fine on our Magnum ME2012 inverter.... it has nothing to do with that, it's more than likely a faulty GFCI outlet, or loose wiring back at the breaker box.
__________________
the Turners...
two Campers, two Electric cars
former diesel pusher traveler
TurnerFam is offline   Reply With Quote
Old 04-03-2018, 03:55 PM   #25
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Maine
Posts: 22
THOR #10229
Thanks for your reply TurnerFam. I am just quoting what a Magnum tech told me on the phone. I had tried numerous new GFI's with the same results. As soon as I changed the GFI to a model the tech told me to, my problem was solved. I never check any other wiring. For me anyway the older non self testing GFI fixed the problem. Maybe your coach doesn't have a self testing GFI and that's why it works.
__________________
Chesuncook1 is offline   Reply With Quote
Old 04-03-2018, 06:52 PM   #26
Senior Member
 
Brand: Thor Motor Coach
State: Georgia
Posts: 2,585
THOR #4735
if by self testing, you mean a red button that reads 'test', then yes, works fine.
__________________
TurnerFam is offline   Reply With Quote
Old 04-03-2018, 07:32 PM   #27
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Maine
Posts: 22
THOR #10229
No, not the red button. Whenever you take power away and then re-energize a new GFI, it goes through a self test which won't work on a modified sine wave inverter. While you are providing power with the inverter, try and push the red test button and then try to reset. Supposedly, that is what you can't do with a modified sine wave inverter. Again, tjis is from Magnum tech not me.
__________________
Chesuncook1 is offline   Reply With Quote
Old 04-03-2018, 08:31 PM   #28
Senior Member
 
Brand: Thor Motor Coach
State: Georgia
Posts: 2,585
THOR #4735
mine's always worked fine, the test button function just like it should, reset sets it back to working.... though, no, no GFCI's will 'test' without power, of course.

apparently some of the new 'automatic' self testing units are too sensitive and don't like certain types of power - I'm also not sure why a 'self testing' unit makes any more sense than the typical GFCI unit - they are all problematic at times, and seem to be overly sensitive. If small children are present, I can understand more reasons for them.
__________________
TurnerFam is offline   Reply With Quote
Old 04-14-2018, 09:25 PM   #29
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3401
State: New York
Posts: 7
THOR #11281
We had the very same gfi problem with our new Aria 3401. It worked fine on 50 amp shore power but kept tripping with anything else. For us this was very serious as the bathroom gfi controls a number of other outlets including the one on the underside of the kitchen over-counter cabinets, where we plug in the coffee maker. I took the suggestion of swapping out the bathroom gfi with a Leviton 8899 (got mine on Amazon for under $20) and that did the trick. With my old fat fingers and very short wires, it was not an easy install but not too bad either.
__________________
Scott & Kathleen
2018 Thor Aria 3401
2015 Mini Roadster toad on Mastertow dolly
ScoWall is offline   Reply With Quote
Old 05-14-2018, 12:48 AM   #30
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Iowa
Posts: 13
THOR #11560
Thank you for your post m1noel. I also own an Aria 3901 with the same GFI tripping problem. Hopefully, this information will come in handy.
__________________
Pirette Tales is offline   Reply With Quote
Old 09-11-2018, 12:10 AM   #31
Junior Member
 
KohTangFred's Avatar
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Iowa
Posts: 17
THOR #12878
GFI Problem Fix

I have had same issue and found the problem in my rig, hope this helps. Aria 3901 2018, The mid bathroom GFI blows all the time, especially when converts from shore power to inverter and back. I have already done most of the fixes I have found posted here including changing the GFI to a 8899, and they didn't help me. The power goes from the bathroom outlet down to the basement where they turn the romax wire over to a stranded wire. then they go up into the passenger side slide and then convert it back to romax wire and up to the outlets. The junction box where they convert back to romax, they take the neutral wire from the cooktop(not GFI or powered by the inverter) and join it with the GFI neutral and then up to the outlet. This junction box is behind the big bottom drawer right under the cooktop.
One of the symptoms that made it hard to figure was when I was on shore power, I had a coffee pot that would blow the GFI the second it was plugged in. on the inverter it wouldn't blow the GFI but would not run anything. If you measured the voltage it showed 114v on the hot, nothing on the ground or neutral. A circuit analyzer shows the outlet was normal when on shore power was on and neutral and hot reversed on inverter.
Hope this helps
Fred
__________________
KohTangFred is offline   Reply With Quote
Old 09-11-2018, 12:24 AM   #32
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Alabama
Posts: 11
THOR #11169
So what was the fix?
__________________
Markewelch is offline   Reply With Quote
Old 09-11-2018, 12:49 AM   #33
Junior Member
 
KohTangFred's Avatar
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Iowa
Posts: 17
THOR #12878
The neutral wire coming from a GFI can't be gang attached or swapped to or with any other neutrals. the neutral coming from the GFI they had terminated (wire nuted off) and then picked up the neutral from the cooktop. Can't do that. Its not uncommon to see all the neutrals in a gang box twisted together which would normally work but not with a GFI circuit. Separate the neutral for the GFI. This won't make sense until you take the drawer out and look in there. In mine the circuit you are looking for was on the left side of the double gang box and marked with a single wrap of black tape. the TV circuit maked with yellow tape Frig was Red tape, cooktop was double black tape. Hope that helps.
__________________
KohTangFred is offline   Reply With Quote
Old 09-11-2018, 12:59 AM   #34
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Alabama
Posts: 11
THOR #11169
I’m going to try this in the morning. I understand you isolated/ separated the neutral for the gfi from the gang. What did you do with it? Did you run a separate ground?
__________________
Markewelch is offline   Reply With Quote
Old 09-11-2018, 01:19 AM   #35
Junior Member
 
KohTangFred's Avatar
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Iowa
Posts: 17
THOR #12878
The wire was there, for whatever the reason they didn't use it. They just put a wire nut on it and left it hanging. I did not mess with the ground... should have looked at it!
Fred
__________________
KohTangFred is offline   Reply With Quote
Old 09-11-2018, 02:38 PM   #36
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Alabama
Posts: 11
THOR #11169
I’m confused Fred: I thought it was a ground issue. Can you please explain exact ally what you did to fix this. Thank you so much.
Mark
__________________
Markewelch is offline   Reply With Quote
Old 09-11-2018, 04:09 PM   #37
Senior Member
 
Brand: Thor Motor Coach
Model: Thor Tuscany 40DX
State: Colorado
Posts: 121
THOR #5043
Small correction from a previous post. The Magnum MS-2012 is a pure sine wave unit so works with a GFI.

MSW units are quite different. Normally the black hot lead from shore power swings in both directions to make a sine wave while the white neutral lead stays at ground. In a MSW the black lead swings positive but then its clamped to zero and the white lead neutral is pulled negative. This results in what approximates a 120V sine wave but totally screws up the GFI. If you put a scope on the whit lead referenced to the green safety ground you'll see this.
__________________
camperguy99 is offline   Reply With Quote
Old 09-12-2018, 01:14 AM   #38
Junior Member
 
KohTangFred's Avatar
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Iowa
Posts: 17
THOR #12878
GFI SIMPLE EXPLANATION
A GFI outlet checks the amount of power going out the black wire (hot) and monitors to see the same amount comes back thru the white wire (neutral) If the amounts differ then it sees this as leaking power because they should match so it trips the GFI. The ground is not monitored but if something shorts out, it shorts to ground to prevent electrocution.
This is why a GFI neutral can't be combined with other neutrals from other circuits.
The ground don't matter in a GFI circuit other than the safety it provides. Thor could have just miswired my unit and that's not why the rest of the Aria 3901's keep blowing the GFI, but the problem I found was part of the loom and I bet there are more done like mine. They can change the GFI's, inverters, etc and the problem isn't going away the way it is wired.
Happy camping
Fred
__________________
KohTangFred is offline   Reply With Quote
Old 09-23-2018, 02:33 AM   #39
Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Arizona
Posts: 66
THOR #11568
Gfi

Mine was kicking all the time. Bought and installed a heavy duty commercial GFI and it has worked fine ever since
__________________
Tebo53AZ is offline   Reply With Quote
Old 10-01-2018, 08:35 PM   #40
Junior Member
 
Brand: Thor Motor Coach
Model: Aria 3901
State: Texas
Posts: 17
THOR #12159
We do have that issue, but now another one. Our windshield was damaged by a hail storm and we ordered a factory one to replace. It was to be put on last Thursday. The one ordered did not fit. The company says it is Thor’s fault due to the shape of the window and Thor said to try another manufacturer. The problem is, we cannot drive the RV and we live in it. Since last Thursday and until someone helps us, we are parked behind a shop owned by Wade's RV in Oklahoma. We are almost ready to quit on our dream of travel. We still get wet in bed when it rains, and we can see outside under the furniture, because no seals were installed inside on the slides. We are not happy with our 2019 Aria 3901, to say the least. We are very positive people, but we are wearing down stuck by a pile of tires and with no septic. : (
__________________
Dr. Terri Edwards
DrTerriEdwards is offline   Reply With Quote
Reply

Tags
3901, aria, electric problem, gfci, gfi, inverter, magnum

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 11:33 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2