Plugging into 110v trips breaker

Hello. We have a 2021 Hurricane 29M. Came with a 50amp cable. When we try to plug into 110 receptacle at our storage facility using a 50amp to 110
Conversion cable, the 110 receptacle with a gfi breaker trips. When I plug in my neighbor’s 30Amp cable into the 110 receptacle the breaker doesn’t trip.
Am i doing something wrong? TIA

__________________
Borismkogan is offline   Reply With Quote
Old 01-23-2021, 11:09 PM   #2
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,326
THOR #7035
This is a common problem. You are tripping the GFCI, not the breaker. Breakers trip on overcurrent.

So the real question is: Why is the coach tripping the GFCI? Because not all the current going out the hot leg is returning on the neutral leg, some is being shunted to ground. This may be due to an actual ground fault (like a screw piercing a hot or neutral conductor) or because some ignorant person tied the ground and neutral lines together in the coach.

Opening all the breakers on your AC power distribution panel will tell you if the former is the problem if it stops the tripping. Then you just need to figure out which circuit has the fault.

Tracing connections with an ohmmeter will help you track down the latter issue.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 01-23-2021, 11:18 PM   #3
Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Washington
Posts: 33
THOR #21575
Quote:
Originally Posted by 16ACE27 View Post
This is a common problem. You are tripping the GFCI, not the breaker. Breakers trip on overcurrent.

So the real question is: Why is the coach tripping the GFCI? Because not all the current going out the hot leg is returning on the neutral leg, some is being shunted to ground. This may be due to an actual ground fault (like a screw piercing a hot or neutral conductor) or because some ignorant person tied the ground and neutral lines together in the coach.

Opening all the breakers on your AC power distribution panel will tell you if the former is the problem if it stops the tripping. Then you just need to figure out which circuit has the fault.

Tracing connections with an ohmmeter will help you track down the latter issue.
Ok I think I follow and sounds like I got something to do tomorrow.... Thanks!
__________________
Borismkogan is offline   Reply With Quote
Old 01-23-2021, 11:50 PM   #4
Senior Member
 
Brand: Thor Motor Coach
Model: Windsport 27K
State: Ohio
Posts: 266
THOR #989
If you determine there is a specific circuit that creates your problem and your 2021 coach is still under warranty I'd have Thor fix the issue.
__________________
John & Diane is offline   Reply With Quote
Old 01-24-2021, 12:40 AM   #5
Senior Member
 
Brand: Thor Motor Coach
Model: Forest River Forester 235
State: Indiana
Posts: 4,884
THOR #6826
It might also just be that one of your GFCI outlets is causing the issue. Sometimes two of them trying to function at the same time will do that. Try just pushing the “test” button your onboard GFCI outlets and leaving them off. I’ll bet that does the trick.
__________________
Pete'sMH is offline   Reply With Quote
Old 01-24-2021, 01:12 AM   #6
Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Washington
Posts: 33
THOR #21575
Quote:
Originally Posted by 16ACE27 View Post
This is a common problem. You are tripping the GFCI, not the breaker. Breakers trip on overcurrent.

So the real question is: Why is the coach tripping the GFCI? Because not all the current going out the hot leg is returning on the neutral leg, some is being shunted to ground. This may be due to an actual ground fault (like a screw piercing a hot or neutral conductor) or because some ignorant person tied the ground and neutral lines together in the coach.

Opening all the breakers on your AC power distribution panel will tell you if the former is the problem if it stops the tripping. Then you just need to figure out which circuit has the fault.

Tracing connections with an ohmmeter will help you track down the latter issue.

Couldn’t wait and went back to the coach and tried your suggestion. Opened all breakers and when I plug in the 110v gfi breaker on my storage space receptacle still trips.
__________________
Borismkogan is offline   Reply With Quote
Old 01-24-2021, 01:13 AM   #7
Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Washington
Posts: 33
THOR #21575
Quote:
Originally Posted by Pete'sMH View Post
It might also just be that one of your GFCI outlets is causing the issue. Sometimes two of them trying to function at the same time will do that. Try just pushing the “test” button your onboard GFCI outlets and leaving them off. I’ll bet that does the trick.

Just so I follow these would be outlets inside the coach? Like in the bathroom perhaps and kitchen?
__________________
Borismkogan is offline   Reply With Quote
Old 01-24-2021, 01:25 AM   #8
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
Quote:
Originally Posted by Borismkogan View Post
Couldn’t wait and went back to the coach and tried your suggestion. Opened all breakers and when I plug in the 110v gfi breaker on my storage space receptacle still trips.
Are you plugging into a GFI outlet?
__________________
Bob Denman is offline   Reply With Quote
Old 01-24-2021, 01:31 AM   #9
Senior Member
 
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
Quote:
Originally Posted by pete'smh View Post
it might also just be that one of your gfci outlets is causing the issue. Sometimes two of them trying to function at the same time will do that. Try just pushing the “test” button your onboard gfci outlets and leaving them off. I’ll bet that does the trick.
Click image for larger version

Name:	What he said in that comment up there (1).jpg
Views:	65
Size:	17.1 KB
ID:	28217
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 01-24-2021, 01:43 AM   #10
Senior Member
 
paulwadley's Avatar
 
Brand: Thor Motor Coach
Model: Miramar 37.1
State: California
Posts: 2,493
THOR #12698
If the 110 outlet is protected by a gfci then that will trip your coach since it too has a gfci. It is a common issue. One gfci is fighting the other gfci.

Paul
__________________
paulwadley is online now   Reply With Quote
Old 01-24-2021, 02:10 AM   #11
Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Washington
Posts: 33
THOR #21575
Quote:
Originally Posted by Bob Denman View Post
Are you plugging into a GFI outlet?

Yes the storage place provides receptacles with gfi
__________________
Borismkogan is offline   Reply With Quote
Old 01-24-2021, 02:11 AM   #12
Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Washington
Posts: 33
THOR #21575
Quote:
Originally Posted by paulwadley View Post
If the 110 outlet is protected by a gfci then that will trip your coach since it too has a gfci. It is a common issue. One gfci is fighting the other gfci.

Paul

How do I disable one fo the GFIs? Would I focus on disabling of the GFI(s) in my coach?
__________________
Borismkogan is offline   Reply With Quote
Old 01-24-2021, 02:21 AM   #13
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Quote:
Originally Posted by Borismkogan View Post
Couldn’t wait and went back to the coach and tried your suggestion. Opened all breakers and when I plug in the 110v gfi breaker on my storage space receptacle still trips.
Opening breakers doesn’t check for a grounded neutral. That’s the most common reason for your problem.

A lot of people think that opening all the circuits should prevent the problem, but it doesn’t. It took an experience electrical engineer to explain why this happens, and he was 100% correct.

First I’d check between neutral and ground at RV to confirm they are not connected in any way.



P.S. — When you opened all breakers, didn’t you kill power to all GFI in motorhome? If so, why did shore-power-source GFI trip? It shouldn’t have if that was issue. I’d confirm ground and neutral are not connected first. Just my 2 cents after going through this problem myself.
__________________
Chance is offline   Reply With Quote
Old 01-24-2021, 02:23 AM   #14
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
I guess if you trip those GFI breakers: your batteries will still be able to take a charge.
I don't think that circuit should be affected.
__________________
Bob Denman is offline   Reply With Quote
Old 01-24-2021, 02:29 AM   #15
Senior Member
 
Brand: Thor Motor Coach
Model: Forest River Forester 235
State: Indiana
Posts: 4,884
THOR #6826
Quote:
Originally Posted by Borismkogan View Post
Just so I follow these would be outlets inside the coach? Like in the bathroom perhaps and kitchen?


Yes, the ones in the coach
__________________
Pete'sMH is offline   Reply With Quote
Old 01-24-2021, 10:47 AM   #16
Senior Member
 
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
Quote:
Originally Posted by Borismkogan View Post
Just so I follow these would be outlets inside the coach? Like in the bathroom perhaps and kitchen?
yes along with the outside outlet and ground-level storage areas.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 01-24-2021, 10:49 AM   #17
Senior Member
 
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
Quote:
Originally Posted by Bob Denman View Post
I guess if you trip those GFI breakers: your batteries will still be able to take a charge.
I don't think that circuit should be affected.
you are correct Bob.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 01-24-2021, 10:55 AM   #18
Senior Member
 
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
Quote:
Originally Posted by Borismkogan View Post
How do I disable one fo the GFIs? Would I focus on disabling of the GFI(s) in my coach?
Either push the test button on the GFI outlet (some rigs have more then one) OR turn off the 15 amp circuit breaker in the panel box labeled GFI. Both of these will turn off any outlet within 6' of a water supply and any ground level storage area. It should allow the shore power GFI circuit to stay intact and supply power to the rest of the RV.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
cavie is offline   Reply With Quote
Old 01-24-2021, 12:44 PM   #19
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Didn’t he try that already?


Quote:
Originally Posted by Borismkogan View Post
Couldn’t wait and went back to the coach and tried your suggestion. Opened all breakers and when I plug in the 110v gfi breaker on my storage space receptacle still trips.
__________________
Chance is offline   Reply With Quote
Old 01-24-2021, 01:00 PM   #20
Senior Member
 
Judge's Avatar
 
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,148
THOR #12751
Quote:
Originally Posted by Chance View Post
Didn’t he try that already?

Sounds like he did......

To the OP..... you said your neighbors 30A doesn't cause it to trip (I assume you mean the same outlet you are trying to use). Have you tried a different 50A to 15A dogbone / adapter? Perhaps the one you are using has a problem. If all of your breakers were open and it tripped when you plugged in, sounds like you either have a problem with your adapter or the 50A cable and / or connections going to the transfer switch.
__________________
Judge is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 02:12 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2