side track...but I'll throw out another device I'm glad to have and would suggest for any new RV
if you have an absorption type fridge
https://www.arprv.com/index.php
__________________
|
|
|
05-29-2020, 01:31 AM
|
#22
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by RudDer1
How did you figure out where to wire it in for both shore and gen? Thanks!
|
Install After the TS. Bur i would not put it there. Won't protect the TS.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-29-2020, 01:35 AM
|
#23
|
Member
Brand: Thor Motor Coach
Model: Windsport 31s
State: Florida
Posts: 54
THOR #18965
|
Clarify
Quote:
Originally Posted by cavie
Install After the TS. Bur i would not put it there. Won't protect the TS.
|
Can you explain "TS" for the newb?
__________________
|
|
|
05-29-2020, 01:41 AM
|
#24
|
Senior Member
Brand: Thor Motor Coach
Model: 2013 31L
State: Florida
Posts: 2,184
THOR #908
|
think they meant "transfer switch"
progressive suggested to install it in the incoming shore power side...first thing the power sees. It's not attached to the genny at all
__________________
|
|
|
05-29-2020, 01:46 AM
|
#25
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by Rey&Reina
Can you explain "TS" for the newb?
|
Transfer switch. Generator will not usually cause any problem. if you put it after TS you can fry the TS. It needs to be the first thing in line.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-29-2020, 01:48 AM
|
#26
|
I Think We're Lost!
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
|
Quote:
Originally Posted by blw2
think they meant "transfer switch"
progressive suggested to install it in the incoming shore power side...first thing the power sees. It's not attached to the genny at all
|
I've heard lots of stories about shore power nightmares; but never one about a generator toasting an electrical system.
__________________
|
|
|
05-29-2020, 03:33 AM
|
#27
|
Senior Member
Brand: Redwood
Model: 36FB
State: Arizona
Posts: 1,766
THOR #3610
|
Quote:
Originally Posted by Bob Denman
The toughest part about locking it to the pedestal is that it adds to the already daunting number of keys you have to keep track of...
(I've also got hitch and trailer tongue locks as well...)
|
There's combination locks available that allow you to set your own combination thereby lightening up your key ring & only 1 combination to remember.
__________________
Fulltimed 10+ years
Sold '13 Thor Redwood 36 FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
|
|
|
05-30-2020, 09:45 AM
|
#28
|
Senior Member
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,154
THOR #12751
|
Ems
Quote:
Originally Posted by Bob Denman
I've heard lots of stories about shore power nightmares; but never one about a generator toasting an electrical system.
|
I have read a few stories about generators not running properly and causing voltage drops and surges.
I’d rather replace a $175 transfer switch than a $1000+ residential fridge or A//C if the generator does malfunction and on the off chance takes a compressor out.
__________________
|
|
|
05-31-2020, 03:08 AM
|
#29
|
Member
Brand: Thor Motor Coach
State: Kansas
Posts: 47
THOR #18734
|
Mine just came in. My directions has two options to install before or after the transfer switch.
__________________
|
|
|
05-31-2020, 12:22 PM
|
#30
|
Senior Member
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,154
THOR #12751
|
Again... I know many people will say put it before the Transfer Switch to protect it but.....
I would rather replace a transfer switch than a $1000+ residential fridge or A/C unit if the generator would have a problem with its output.
Also.... under the "stuff" happens category...... if a transfer switch ever malfunctioned (contacts sticking closed on one side, etc.), could the TS allow both shore power and generator power to flow simultaneously if they were both present? If so, 240V could be sent from the TS and through the rig frying a lot of electronic equipment. The EMS would prevent that from ever happening.
If the EMS is placed after the transfer switch, the coach electronics are fully protected from any potential power input issues.
In hindsight..... I might have replaced the stock transfer switch with one that has built in surge protection like this one... https://rvpower.southwire.com/produc...h-model-40450/
But even still... the power is touching the relays before the surge protection can assess the quality of the power... but it is also protecting the power from the generator.
__________________
|
|
|
05-31-2020, 01:04 PM
|
#31
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by blw2
progressive industries is the only way to go based on my research several years ago. I installed a hardwired one.
My only regret was that I installed it without the remote display in a place where it's hard to get at. (under the bed and the slide has to be out to lift it)
anyway, it's not a huge issue....and I'm glad to have the device
|
Hughes Watch Dog is the new kid on the block. Has Blue tooth.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-31-2020, 01:05 PM
|
#32
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by Judge
Again... I know many people will say put it before the Transfer Switch to protect it but.....
I would rather replace a transfer switch than a $1000+ residential fridge or A/C unit if the generator would have a problem with its output.
Also.... under the "stuff" happens category...... if a transfer switch ever malfunctioned (contacts sticking closed on one side, etc.), could the TS allow both shore power and generator power to flow simultaneously if they were both present? If so, 240V could be sent from the TS and through the rig frying a lot of electronic equipment. The EMS would prevent that from ever happening.
If the EMS is placed after the transfer switch, the coach electronics are fully protected from any potential power input issues.
|
50 amp rigs ARE 240 volts.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-31-2020, 01:13 PM
|
#33
|
Senior Member
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,154
THOR #12751
|
Quote:
Originally Posted by cavie
50 amp rigs ARE 240 volts.
|
120V on each leg..... I'm talking about putting 240V on each leg.... which is what the EMS can protect..... Should one relay stuck closed and allow power to flow from it when the other relay was called to engaged and power to both inputs of the TS was present and flowed into the coach putting 240V on each leg.
__________________
|
|
|
05-31-2020, 02:01 PM
|
#34
|
Senior Member
Brand: Thor Motor Coach
Model: '17-Vegas 24.1
State: California
Posts: 2,227
THOR #13362
|
My Progressive EMS is installed after the Transfer Switch, just as Progressive recommends.
Right after installation, I read a post by a fellow Vegas owner who had a generator alternator malfunction. It kept shutting down the EMS.
After analysis, he found that the generator voltage controller malfunctioned, and was sending 170 volts to his RV.
He credits the fact that his RV was saved because he hardwired a Surge Guard after the Transfer Switch.
And, oh by the way...the Transfer Switch was unharmed.
https://youtu.be/xu35A2YwYG8
__________________
'17 Vegas 24.1
Fallbrook, CA
|
|
|
05-31-2020, 02:46 PM
|
#35
|
Senior Member
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,154
THOR #12751
|
Quote:
Originally Posted by taylorbob1
My Progressive EMS is installed after the Transfer Switch, just as Progressive recommends.
Right after installation, I read a post by a fellow Vegas owner who had a generator alternator malfunction. It kept shutting down the EMS.
After analysis, he found that the generator voltage controller malfunctioned, and was sending 170 volts to his RV.
He credits the fact that his RV was saved because he hardwired a Surge Guard after the Transfer Switch.
And, oh by the way...the Transfer Switch was unharmed.
https://youtu.be/xu35A2YwYG8
|
That is the way I have it wired as well.
__________________
|
|
|
05-31-2020, 03:01 PM
|
#36
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by Judge
120V on each leg..... I'm talking about putting 240V on each leg.... which is what the EMS can protect..... Should one relay stuck closed and allow power to flow from it when the other relay was called to engaged and power to both inputs of the TS was present and flowed into the coach putting 240V on each leg.
|
You can not physically get 240 on one leg in the US. 240 is on one leg in Europe.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-31-2020, 03:09 PM
|
#37
|
I Think We're Lost!
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
|
Wouldn't you need a whole lot bigger cables to handle a load like that?
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
|
|
|
05-31-2020, 04:22 PM
|
#38
|
Senior Member
Brand: Thor Motor Coach
Model: 2020 Magnitude SV34
State: Florida
Posts: 4,154
THOR #12751
|
Ems
Quote:
Originally Posted by cavie
You can not physically get 240 on one leg in the US. 240 is on one leg in Europe.
|
So your saying if the Generator is putting out 120 V on each leg and then you add a second 120V source to each of the same legs, it’s not gong to do any damage from over voltage condition.
__________________
|
|
|
05-31-2020, 04:24 PM
|
#39
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,422
THOR #15553
|
Quote:
Originally Posted by Bob Denman
Wouldn't you need a whole lot bigger cables to handle a load like that?
|
Just the opposite. Large voltage small wire. large amperage bigger wire.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
05-31-2020, 04:37 PM
|
#40
|
I Think We're Lost!
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
|
Quote:
Originally Posted by cavie
Just the opposite. Large voltage small wire. large amperage bigger wire.
|
Thanks! I barely know which part of the fork to NOT stick in the electrical socket!