Old 05-26-2017, 03:47 AM   #41
Member
 
anijet's Avatar
 
Brand: DRV
Model: 36TK3
State: California
Posts: 64
THOR #2059
Quote:
Originally Posted by gmc View Post
I know this changed with later readings - but nothing will 'overload' if it were the case... It is exactly what a 30A to 50A adapter does - it bridges the same single hot to both 'line' contacts - the neutral can still never see more than 50A because the single 50A breaker will trip.

Whether you really have access to 50A or 100A total depends on how the pedestal was wired and whether you are using an adapter in the line.

At new home right now I'm using a 30A to 50A adapter - until I get the new '50A' line run...
Line 1 to Neutral = 110v
Line 2 to Neutral = 110v
Line 1 to Line 2 = 0v (both are same live wire - no flow of electricity...)

I don't believe even wiring a pedestal this way violates any code (at least if it were a single pole 50A breaker...) and does provide '50 amps' - it just doesn't provide 100 amps... likely to be the parks argument.

Rigs that need a true 220V (like for the 220v dryer mentioned) wouldn't work in that setup... Wouldn't hurt it - just wouldn't power the 220V appliances.
What was being considered was IF the same 120vac line was run to both 50 amp breakers and each breaker was connected to each line contact on a 50 amp outlet you could see 100 amps on the ships neutral.

__________________
2007 MS 36 TK3, Demco Glide Ride
2012 GMC 3500HD D/A CC, AirSafe Hitch
anijet is offline   Reply With Quote
Old 05-26-2017, 01:21 PM   #42
Senior Member
 
Brand: DRV
Model: 44' Santa Fe
State: Montana
Posts: 392
THOR #2053
gmc=it does violate the NEC since the outlet in question is a 50a 120/250 volt device. The / in the equation means it is REQUIRED to supply 120 AND 250 volt max., not just 120volt. At least in every jurisdiction I've ever worked in. I was an EE and licensed as an EE & master electrician in 17 states, Canada and Mexico.
The neutral could be overloaded in the above case IF it was fed from two separate 50 amp breakers on the same phase. 50 + 50 still equals 100. The probability of anyone in an rv drawing that much current is highly doubtful, but is possible. In this case you would not be using a dog bone (which are perfectly safe) but plugging into a mis wired outlet.
Would it "hurt" being miswired in this fashion? Probably not, and would allow for more current draw than a dog bone would, but still a NEC violation and should be rejected by any inspector worth their pay.

Bill
__________________
Porkchop is offline   Reply With Quote
Old 05-26-2017, 02:52 PM   #43
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
What I'm curious to learn now is whether these add-on surge protection devices are designed to trip "IF" a 50-Amp was wired wrong with both legs in phase? And if not, do they monitor current in neutral conductor to prevent damage to RV?
__________________
Chance is offline   Reply With Quote
Old 05-26-2017, 04:48 PM   #44
Senior Member
 
Brand: DRV
Model: 44' Santa Fe
State: Montana
Posts: 392
THOR #2053
Basically NO they will not trip solely because they find that both legs are on the same phase. They will read the situation and decide that it plugged into a 30 amp device. They do not trip on over current, that is the job of the circuit breaker. And no, they do not monitor the return current on the neutral. Only that one is present. That would be the job of either a gfci or arc fault breaker. And they would only trip when there was too little return current, not too much.

Bill
__________________
Porkchop is offline   Reply With Quote
Old 05-28-2017, 04:37 PM   #45
Senior Member
 
RustyJC's Avatar
 
Brand: DRV
Model: Mobile Suites 38RSSA
State: Texas
Posts: 206
THOR #2754
The power management system on our Mobile Suites 38RSSA will default to 30 amp service if it does not see 240vac across L1 and L2. In this mode, it will not permit the 2nd A/C compressor to engage, and it will load shed. I have firsthand knowledge of this since the 50 amp receptacle in the wash rack at the storage facility we use is miswired with both hot legs on the same phase.

Rusty
__________________
Rusty, Sandy, 2 Shelties (Coby & Callie) & Conner the Campground Cat
2016 Ram 3500 Longhorn Crew Cab 4x4 Dually, 385/900 Cummins, Aisin AS69RC, 4.10 axle, 39,100 GCWR, 30,050 trailer tow, B&W RVK3600
Current: 2014.5 DRV Mobile Suites 38RSSA #6972 - Previous: 2004 MS 36RE3 #1291
RustyJC is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 04:32 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2