Quote:
Originally Posted by RockyTee
New guy here...2020 Thor ACE 30.1. For some reason, I'm not getting any propane to the stove or furnace. I turned it on at the tank and get nothing inside. This is a new coach. Am I missing a valve someplace?
|
See post #5. There is a pressure balance valve in the regulator line. It is there to cut-off propane in the event of a line break or puncture, as in a wreck, rock or overturn. If the propane lines are empty (no pressure) and you crank the valve open all at once, the pressure balance valve will sense a loss of pressure and seal the tank. Fortunately, the vale is self-resetting (they were not self-resetting in the old days). If you turn the propane tank valve completely off and wait for 30 minutes for the pressure to bled off and the valve reset; then open the tank's shut-off VERY slowly it will pressurize the system to 11 inches of water.