Old 07-03-2022, 10:36 PM   #1
Junior Member
 
Brand: Thor Motor Coach
State: Minnesota
Posts: 13
THOR #26172
2022 Thor Sequence and generator use

Hi,

Does anyone know why I’d be getting an error message when plugging a 2022 Thor Sequence into a portable generator? The error message is “Shore Power Fault. The power cord has been connected to a faulty power source. Power will not be restored until connected to a properly working source.”

__________________
Babyjakejake is offline   Reply With Quote
Old 07-03-2022, 10:38 PM   #2
MLP
Senior Member
 
Brand: Thor Motor Coach
State: California
Posts: 890
THOR #17478
On a lot of generators, you must tie the ground to neutral at the generator. Some make a plug that does just that.
__________________
2013 Thor Palazzo 33.2
2013 Honda CRV
MLP is offline   Reply With Quote
Old 07-03-2022, 10:43 PM   #3
Junior Member
 
Brand: Thor Motor Coach
State: Minnesota
Posts: 13
THOR #26172
Quote:
Originally Posted by MLP View Post
On a lot of generators, you must tie the ground to neutral at the generator. Some make a plug that does just that.
Sorry, total newbie here. How do you tie the ground to neutral at the generator? We couldn’t plug directly into the generator with the RV power cord because it was a different plug on. So we did buy a converter that allows us to plug into the generator. Is that what you mean?
__________________
Babyjakejake is offline   Reply With Quote
Old 07-03-2022, 11:13 PM   #4
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,326
THOR #7035
Quote:
Originally Posted by Babyjakejake View Post
Sorry, total newbie here. How do you tie the ground to neutral at the generator? We couldn’t plug directly into the generator with the RV power cord because it was a different plug on. So we did buy a converter that allows us to plug into the generator. Is that what you mean?
No, the adapter has nothing to do with it. This is all in the generator. The error is because it expects to see the neutral and ground bonded in the power source. There are "bonding" plugs that you can use to plug into the 15 amp outlet on the generator to accomplish this or you can follow your generator's instructions in its manual to bond the ground and neutral.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 07-03-2022, 11:34 PM   #5
Junior Member
 
Brand: Thor Motor Coach
State: Minnesota
Posts: 13
THOR #26172
Quote:
Originally Posted by 16ACE27 View Post
No, the adapter has nothing to do with it. This is all in the generator. The error is because it expects to see the neutral and ground bonded in the power source. There are "bonding" plugs that you can use to plug into the 15 amp outlet on the generator to accomplish this or you can follow your generator's instructions in its manual to bond the ground and neutral.

Thanks Ted and Melinda for your help! I will give this a try.
__________________
Babyjakejake is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 08:22 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2