Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 

Go Back   Thor Forums > Thor Motorcoach & Motorhome > Thor Motorhome General Discussions
Click Here to Login
Closed Thread
 
Thread Tools Display Modes
 
Old 09-12-2024, 09:41 PM   #1
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
generator priority?

Today I started my generator while I was connected to shore power. After a few seconds, I heard beeps from my inverter/charger. This tells me that my ATS (automatic transfer switch) is wired for generator priority. Why?

I would like the generator to be ignored when shore power is available.

Is there any reason that I shouldn't re-wire the ATS so it gives priority to shore power? What am I not considering?

__________________
Wiley1 is offline  
Old 09-12-2024, 09:55 PM   #2
Member
 
Brand: Thor Motor Coach
Model: Omni RS36
State: California
Posts: 48
THOR #30872
My theory, say you are plugged into shore power and the power supply is insufficient for the devises you plan to run, you could start your generator and it would power it. For example, you are plugged into a 30amp plug at a campsite, but you have a 50amp RV and you are concerned about not having enough juice to power her hairdryer, the coffee maker and microwave when you are making breakfast.
__________________
PSDtime is offline  
Old 09-12-2024, 09:57 PM   #3
Senior Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Texas
Posts: 2,943
THOR #11781
Quote:
Originally Posted by PSDtime View Post
My theory, say you are plugged into shore power and the power supply is insufficient for the devises you plan to run, you could start your generator and it would power it. For example, you are plugged into a 30amp plug at a campsite, but you have a 50amp RV and you are concerned about not having enough juice to power her hairdryer, the coffee maker and microwave when you are making breakfast.
Bingo.
__________________
Lt Keefer
2018 Hurricane 29M
CHF, Saf-T-Plus, SumoSprings
Lt Keefer is offline  
Old 09-12-2024, 10:13 PM   #4
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
Quote:
Originally Posted by PSDtime View Post
My theory, say you are plugged into shore power and the power supply is insufficient for the devises you plan to run, you could start your generator and it would power it. For example, you are plugged into a 30amp plug at a campsite, but you have a 50amp RV and you are concerned about not having enough juice to power her hairdryer, the coffee maker and microwave when you are making breakfast.
Sure, but you could also unplug the shore power.
My rig is 30A. If the shore power is really dirty, that's exactly what I would do.
__________________
Wiley1 is offline  
Old 09-12-2024, 10:30 PM   #5
Senior Member
 
dkoldman's Avatar
 
Brand: Still Looking
Model: Sunstar 29VE Winnebago
State: Texas
Posts: 6,436
THOR #13058
Quote:
Originally Posted by Wiley1 View Post
Today I started my generator while I was connected to shore power. After a few seconds, I heard beeps from my inverter/charger. This tells me that my ATS (automatic transfer switch) is wired for generator priority. Why?

I would like the generator to be ignored when shore power is available.

Is there any reason that I shouldn't re-wire the ATS so it gives priority to shore power? What am I not considering?
I agree with all of the above about the why, but I will answer your question in red.

Yes, you can wire your coach so the generator will be ignored if Shorepower is On. But you require a AGS system that is capable to do so.

I had my coach wired this way when it was brand new. It was actually my 1st mod.

It works like this...

I have Onan EC-30 AGS system
I had a 24vdc transformer put on the inbound SP line IN FRONT of ATS. The transformer send signal direct to the EC-30 so the EC-30 always knows if SP is on or off. It does bot care if it 50amp, 30amps or 20amps.
If your have your AGS configured properly an in the Auto or Quiet mode, it will not allow you to start the generator if SP exist. If you want to run the genny, you must unplug or simple take the AGS out of AUTO or Quiet Time mode.

The other thing that is neat and I admit I do for play, but say you pull up to park RV, set levelers etc. My engine continues to run as well as the ACs. When I plug up SP it will automatically shut the genny off
__________________
2019 Sunstar 29ve; Toad Lincoln Navigator; RVi Brake 3, Tire Patrol & Command Center; Roadmaster Nighthawk Tow bar & Baseplate; Sumo Springs; Safe T Plus; Onan EC-30 AGS; 300ah Lithium; Victron Orion XS & SmartShunt; T-Mobile Internet; H/W Heater / Chassis Disconnect Switches; Southwire Surge Guard 44270 & 34951 w/Monitor 40301; Jet Flo Macerator; Alpine SPE500 Speakers; Visio M21D-H8R
dkoldman is online now  
Old 09-12-2024, 10:58 PM   #6
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 15,909
THOR #7035
Quote:
Originally Posted by Wiley1 View Post
Today I started my generator while I was connected to shore power. After a few seconds, I heard beeps from my inverter/charger. This tells me that my ATS (automatic transfer switch) is wired for generator priority. Why?

I would like the generator to be ignored when shore power is available.

Is there any reason that I shouldn't re-wire the ATS so it gives priority to shore power? What am I not considering?
The real question is:

Why are you running the generator if you don't want it to power the RV?
__________________
Ted & Melinda
2016 ACE 27.1
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B BU TOAD
16ACE27 is offline  
Old 09-12-2024, 11:15 PM   #7
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
Quote:
Originally Posted by dkoldman View Post
Yes, you can wire your coach so the generator will be ignored if Shorepower is On. But you require a AGS system that is capable to do so.
I'm sure your AGS is wonderful, but I don't see how it has anything to do with my situation or the question that I asked.

An 30A RV ATS is a dumb switch, capable of only one decision. When power is available on port A, it is passed through to the output. When no power is available on port A, whatever power is (or isn't) available on port B is passed through to the output. Simple Whatever is connected to port A becomes the priority.

The output of the ATS (120vac, either from the genny or the shore cable) connects to the input of my 3000kW inverter/charger. That device really doesn't know or care where the power came from as long as it is clean.

I am proposing that I swap cable A with cable B so that shore-power is selected by default. I am having difficulty imagining any situation where generator power would be preferred over shore-power.

I came here only to ask if anyone sees any flaw in my plan.
__________________
Wiley1 is offline  
Old 09-12-2024, 11:20 PM   #8
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 15,909
THOR #7035
Quote:
Originally Posted by Wiley1 View Post
I'm sure your AGS is wonderful, but I don't see how it has anything to do with my situation or the question that I asked.

An 30A RV ATS is a dumb switch, capable of only one decision. When power is available on port A, it is passed through to the output. When no power is available on port A, whatever power is (or isn't) available on port B is passed through to the output. Simple Whatever is connected to port A becomes the priority.

The output of the ATS (120vac, either from the genny or the shore cable) connects to the input of my 3000kW inverter/charger. That device really doesn't know or care where the power came from as long as it is clean.

I am proposing that I swap cable A with cable B so that shore-power is selected by default. I am having difficulty imagining any situation where generator power would be preferred over shore-power.

I came here only to ask if anyone sees any flaw in my plan.
Turn off the generator - mission accomplished.

Again - why run the generator if you don't want power from it?

What am I missing??
__________________
Ted & Melinda
2016 ACE 27.1
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B BU TOAD
16ACE27 is offline  
Old 09-12-2024, 11:24 PM   #9
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
Quote:
Originally Posted by 16ACE27 View Post
The real question is:
Why are you running the generator if you don't want it to power the RV?
How is that "the real question"?
There's always somebody who wants to change the question to something else. But, I'm happy to answer.

Today I just wanted to test and exercise the generator. That would be reason enough.

For the first five minutes, the generator oscillated fast/slow/fast/slow. That drove my inverter/charger nuts, and it switched over to battery power and back several times. In that situation, I would like the wonky generator power to be ignored.

The real real question is:
Is there any reason that shore-power should not be the priority?
__________________
Wiley1 is offline  
Old 09-12-2024, 11:51 PM   #10
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 15,909
THOR #7035
Quote:
Originally Posted by Wiley1 View Post
How is that "the real question"?
There's always somebody who wants to change the question to something else. But, I'm happy to answer.

Today I just wanted to test and exercise the generator. That would be reason enough.

For the first five minutes, the generator oscillated fast/slow/fast/slow. That drove my inverter/charger nuts, and it switched over to battery power and back several times. In that situation, I would like the wonky generator power to be ignored.

The real real question is:
Is there any reason that shore-power should not be the priority?
The same reason your wonky generator power shouldn't be sent to the load buss. If you have generator running problems to iron out and don't want the generator loaded, open the generator output breaker.

To exercise the generator it needs to be loaded at 1/2 capacity for at least an hour.
__________________
Ted & Melinda
2016 ACE 27.1
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B BU TOAD
16ACE27 is offline  
Old 09-13-2024, 01:40 AM   #11
Site Team
 
EA37TS's Avatar
 
Brand: Entegra
Model: Accolade 37TS
State: South Dakota
Posts: 8,939
THOR #1469
If I recall correctly a few years ago at the FMCA Convention in Wyoming, during an Onan generator seminar, an Inan Engineer mentioned why an RV ATS is wired to give priority to the generator and why shore power should be disconnected before starting the generator.

Contact Onan and ask them if your idea will have any impact on the generator.
__________________
EA37TS is offline  
Old 09-13-2024, 01:55 AM   #12
Senior Member
 
dkoldman's Avatar
 
Brand: Still Looking
Model: Sunstar 29VE Winnebago
State: Texas
Posts: 6,436
THOR #13058
Quote:
Originally Posted by Wiley1 View Post
I'm sure your AGS is wonderful, but I don't see how it has anything to do with my situation or the question that I asked.

An 30A RV ATS is a dumb switch, capable of only one decision. When power is available on port A, it is passed through to the output. When no power is available on port A, whatever power is (or isn't) available on port B is passed through to the output. Simple Whatever is connected to port A becomes the priority.

The output of the ATS (120vac, either from the genny or the shore cable) connects to the input of my 3000kW inverter/charger. That device really doesn't know or care where the power came from as long as it is clean.

I am proposing that I swap cable A with cable B so that shore-power is selected by default. I am having difficulty imagining any situation where generator power would be preferred over shore-power.

I came here only to ask if anyone sees any flaw in my plan.
The answer to your question in post above is below, and is direct to your 1st post question.

YOU STATED: I would like the generator to be ignored when shore power is available.

Is there any reason that I shouldn't re-wire the ATS so it gives priority to shore power? What am I not considering?


My post agreed by saying I too like having my generator IGNORED when shore power is available.

I then went a step further and show you exactly how I do it.

You also asked if you shouldn't rewire, my method did involve a rewire.

Then you also asked what you were not considering, I told you of an option to use an AGS as it will do that for you automatically.


But with that said, it obvious that is not want you wanted to hear/read. Of course I would have no way of knowing that, I was just answering your questions.
__________________
2019 Sunstar 29ve; Toad Lincoln Navigator; RVi Brake 3, Tire Patrol & Command Center; Roadmaster Nighthawk Tow bar & Baseplate; Sumo Springs; Safe T Plus; Onan EC-30 AGS; 300ah Lithium; Victron Orion XS & SmartShunt; T-Mobile Internet; H/W Heater / Chassis Disconnect Switches; Southwire Surge Guard 44270 & 34951 w/Monitor 40301; Jet Flo Macerator; Alpine SPE500 Speakers; Visio M21D-H8R
dkoldman is online now  
Old 09-13-2024, 02:59 AM   #13
Senior Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Texas
Posts: 2,943
THOR #11781
There are a number of threads on this issue on IRV2. Maybe the answer is there as I didn't read them all. I like my genny to be dominant but then I have a 50 amp coach that sometimes gets 30 amp shore power.
__________________
Lt Keefer
2018 Hurricane 29M
CHF, Saf-T-Plus, SumoSprings
Lt Keefer is offline  
Old 09-13-2024, 01:42 PM   #14
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
Quote:
Originally Posted by 16ACE27 View Post
The same reason your wonky generator power shouldn't be sent to the load buss. If you have generator running problems to iron out and don't want the generator loaded, open the generator output breaker.

To exercise the generator it needs to be loaded at 1/2 capacity for at least an hour.
That is useful information but, again, not relevant to my question.

1. My generator doesn't perform well for the first five minutes. Until it warms up, I don't want my inverter/charger to be exposed to that unstable waveform.
2. I do not have a "generator output breaker".
3. Once the generator has warmed up and the output is stable, if I want to load it, all I have to do is unplug the shore power cable.

So far, nobody has mentioned a good reason not to make shore power the priority.
__________________
Wiley1 is offline  
Old 09-13-2024, 01:44 PM   #15
Senior Member
 
Brand: Thor Motor Coach
Model: Freedom Elite 23H
State: Virginia
Posts: 259
THOR #19277
Quote:
Originally Posted by Lt Keefer View Post
There are a number of threads on this issue on IRV2. Maybe the answer is there as I didn't read them all.
Thank you for that. I will definitely go over there and read that thread. Perhaps those guys are better at staying on topic.
__________________
Wiley1 is offline  
Old 09-13-2024, 03:19 PM   #16
MCP
Senior Member
 
Brand: Thor Motor Coach
Model: Tellaro 20k
State: Arizona
Posts: 287
THOR #27962
Quote:
Originally Posted by Wiley1 View Post
Thank you for that. I will definitely go over there and read that thread. Perhaps those guys are better at staying on topic.
I don’t want to risk pissing anyone off by not giving a precise answer, but have you contacted Southwiire or whoever your ATS mfr is? They can answer your first question of why is their product and wiring instructions set up that way. Perhaps it is not a technical issue and it’s only an industry standard because most are used in that manner.

If it is not a technical requirement then give it a try and let us know how it goes. That’s my nonprecise answer to your second question.
__________________
MCP is offline  
Old 09-13-2024, 06:29 PM   #17
Senior Member
 
Brand: Thor Motor Coach
Model: Hurricane 31S
State: Texas
Posts: 4,397
THOR #6411
The ATS primary function is to prevent the unplugged shore line from becoming hot when the generator is started. In the old days (I had a 1968 class A coach) shore lines were connected directly to the coach and we had to manually transfer the coach's input from the shore line receptacle to the generator receptacle. The receptacles were in the closet beside the 120 volt CB box.


I don't know about all coaches but my ATS (PPS) has a generator delay that is user settable from 20 seconds to 120 seconds and the EMS had an additional delay of 15 seconds and 136 seconds.
__________________
Jim & Roy Davis
2016 Hurricane 31S
1961 Rampside in tow
Beau388 is offline  
Old 09-13-2024, 07:26 PM   #18
Senior Member
 
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Texas
Posts: 2,943
THOR #11781
Quote:
Originally Posted by Beau388 View Post
The ATS primary function is to prevent the unplugged shore line from becoming hot when the generator is started. In the old days (I had a 1968 class A coach) shore lines were connected directly to the coach and we had to manually transfer the coach's input from the shore line receptacle to the generator receptacle. The receptacles were in the closet beside the 120 volt CB box.


I don't know about all coaches but my ATS (PPS) has a generator delay that is user settable from 20 seconds to 120 seconds and the EMS had an additional delay of 15 seconds and 136 seconds.
That makes sense. It may be possible, however unlikely, that a running generator could put power to the shore power cable. In my last coach, the generator only powered a plug in the shore power cable storage compartment.
__________________
Lt Keefer
2018 Hurricane 29M
CHF, Saf-T-Plus, SumoSprings
Lt Keefer is offline  
Old 09-13-2024, 07:48 PM   #19
Senior Member
 
RACarvalho's Avatar
 
Brand: Thor Motor Coach
Model: Hurricane 34R
State: Indiana
Posts: 663
THOR #19887
Quote:
Originally Posted by Wiley1 View Post
Is there any reason that I shouldn't re-wire the ATS so it gives priority to shore power? What am I not considering?
Besides the reason given so far, I really like Generator priority:
I want to have the generator on when I move the slides before departing and that also means the generator will be powering the ACs....
So after I put the slides in and retract the jacks, all while the ACs are on, I don't need to turn off the ACs before I disconnect the power cord, I just go outside, disconnect the power cord (the last step before departing), store it and go... all while the AC is running...
__________________

Videos of some of our trips:
https://rumble.com/c/c-751683
RACarvalho is offline  
Old 09-13-2024, 09:26 PM   #20
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 15,909
THOR #7035
Quote:
Originally Posted by Wiley1 View Post
That is useful information but, again, not relevant to my question.

1. My generator doesn't perform well for the first five minutes. Until it warms up, I don't want my inverter/charger to be exposed to that unstable waveform.
2. I do not have a "generator output breaker".
3. Once the generator has warmed up and the output is stable, if I want to load it, all I have to do is unplug the shore power cable.

So far, nobody has mentioned a good reason not to make shore power the priority.
Just because you are ignorant of the generator output breaker does not mean it does not exist - it does.

Why would your Onan generator be different than every other one made and installed in an RV?
__________________
Ted & Melinda
2016 ACE 27.1
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B BU TOAD
16ACE27 is offline  
Closed Thread

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 04:53 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2