Onan 5500 Genset Uncommanded Shut Down
Good evening! My 2015 Thor Windsport 32n is equipped with a Onan 5500 GENSET. It has had all the right care but now it has decided to do shut off totally on its own without any command from me. There is no sign of overheating or other visible issues. We have been using the MH quite a bit and have run many gallons of gas through the tank. We live in central Florida and it has not been sitting in storage. I have put an additive in the tank to help keep the ethanol byproducts from building up in both the coach fuel injectors and the GENSET carb. It has just over 200 original hours on the meter.
Does any one have any suggestions as to why it is acting up? Looking forward to see what suggestions are out there.
Thanks,
AFLOGGIE
__________________
|
|
|
03-23-2023, 11:32 PM
|
#2
|
Senior Member
Brand: Thor Motor Coach
Model: Vegas 25.6
State: New Mexico
Posts: 3,998
THOR #20220
|
Quote:
Originally Posted by AFLOGGIE
Good evening! My 2015 Thor Windsport 32n is equipped with a Onan 5500 GENSET. It has had all the right care but now it has decided to do shut off totally on its own without any command from me. There is no sign of overheating or other visible issues. We have been using the MH quite a bit and have run many gallons of gas through the tank. We live in central Florida and it has not been sitting in storage. I have put an additive in the tank to help keep the ethanol byproducts from building up in both the coach fuel injectors and the GENSET carb. It has just over 200 original hours on the meter.
Does any one have any suggestions as to why it is acting up? Looking forward to see what suggestions are out there.
Thanks,
AFLOGGIE
|
Cummins does fixes and gave us a 2 year warranty
__________________
|
|
|
03-23-2023, 11:45 PM
|
#3
|
Senior Member
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,173
THOR #11130
|
Oil level? They are pretty sensitive to this.
__________________
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
|
|
|
03-23-2023, 11:50 PM
|
#4
|
Site Team
Brand: Entegra
Model: Accolade 37TS
State: South Dakota
Posts: 8,054
THOR #1469
|
8 years old and only 200 hours the generator suffers from neglect. More than likely you need to redo the entire fuel system.
__________________
|
|
|
03-23-2023, 11:54 PM
|
#5
|
Junior Member
Brand: Thor Motor Coach
Model: Thor Windsport
State: Florida
Posts: 26
THOR #28183
|
Thanks!
__________________
|
|
|
03-23-2023, 11:55 PM
|
#6
|
Junior Member
Brand: Thor Motor Coach
Model: Thor Windsport
State: Florida
Posts: 26
THOR #28183
|
Is a rebuild a big project or should I let the professionals do it?
__________________
|
|
|
03-23-2023, 11:56 PM
|
#7
|
Junior Member
Brand: Thor Motor Coach
Model: Thor Windsport
State: Florida
Posts: 26
THOR #28183
|
Oil level is better than 3/4 up the dip stick well within the safety zone on the dipstick.
__________________
|
|
|
03-23-2023, 11:57 PM
|
#8
|
Senior Member
Brand: Thor Motor Coach
Model: Hurricane 31S
State: Texas
Posts: 3,804
THOR #6411
|
Quote:
Originally Posted by EA37TS
8 years old and only 200 hours the generator suffers from neglect. More than likely you need to redo the entire fuel system.
|

__________________
Jim & Roy Davis
2016 Hurricane 31S
1961 Rampside in tow
|
|
|
03-23-2023, 11:58 PM
|
#9
|
Senior Member
Brand: Still Looking
Model: Sunstar 29VE Winnebago
State: Texas
Posts: 4,332
THOR #13058
|
When you call Onan, I don't think they will consider 25 hours / year a lot of usage. Maybe if all you ever did was exercise it?
I would start by trying to get the error code. If you don't have a EC-30 you may need Onan manual or Onan Support to help to see why it is shutting down.
__________________
2019 Sunstar 29VE Sumo Springs; Safe T Plus; EC-30 AGS; Vmax 250ah AGM; T-Mobile Internet w/WiFi6; H/W Heater / Chassis Disconnect Switches; Southwire Surge Guard 44270 & 34951 w/Monitor 40301; Jet Flo Macerator; Alpine SPE500 Speakers; Visio M21D-H8R
|
|
|
03-24-2023, 12:13 AM
|
#10
|
Site Team
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 11,708
THOR #7035
|
Quote:
Originally Posted by AFLOGGIE
Good evening! My 2015 Thor Windsport 32n is equipped with a Onan 5500 GENSET. It has had all the right care but now it has decided to do shut off totally on its own without any command from me. There is no sign of overheating or other visible issues. We have been using the MH quite a bit and have run many gallons of gas through the tank. We live in central Florida and it has not been sitting in storage. I have put an additive in the tank to help keep the ethanol byproducts from building up in both the coach fuel injectors and the GENSET carb. It has just over 200 original hours on the meter.
Does any one have any suggestions as to why it is acting up? Looking forward to see what suggestions are out there.
Thanks,
AFLOGGIE
|
Get your generator model number
Get your generator manual online
Review the procedure to extract trouble codes.
Next time it shuts down pull the trouble codes and follow the manual. Much better than guessing.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad
2020 Chevy Colorado Z71 Trail Runner Alternate Toad
|
|
|
03-24-2023, 12:53 AM
|
#11
|
Senior Member
Brand: Thor Motor Coach
Model: Hurricane 29M
State: Texas
Posts: 2,306
THOR #11781
|
You need a manual or possibly an actual Cummins mechanic, not a silver bullet from the internet.
__________________
Lt Keefer
2018 Hurricane 29M
CHF, Saf-T-Plus, SumoSprings
|
|
|
03-24-2023, 01:10 AM
|
#12
|
Senior Member
Brand: Thor Motor Coach
Model: Winnebago Travato 59G
State: Alabama
Posts: 4,762
THOR #6826
|
Quote:
Originally Posted by EA37TS
8 years old and only 200 hours the generator suffers from neglect. More than likely you need to redo the entire fuel system.
|
Seems about right though if it’s just getting exercised properly. 2 hrs/month for 8 years.
__________________
|
|
|
03-24-2023, 01:15 AM
|
#13
|
Senior Member
Brand: Thor Motor Coach
Model: Winnebago Travato 59G
State: Alabama
Posts: 4,762
THOR #6826
|
Before spending money at Onan try basic engine troubleshooting. Disconnect the fuel line and see if the pump is pumping. Check the fuel filter, check or simply replace the spark plug and check the wiring, especially the ground connection etc.
__________________
|
|
|
03-24-2023, 01:16 AM
|
#14
|
Site Team
Brand: Entegra
Model: Accolade 37TS
State: South Dakota
Posts: 8,054
THOR #1469
|
Quote:
Originally Posted by Pete'sMH
Seems about right though if it’s just getting exercised properly. 2 hrs/month for 8 years.
|
The Onan folks will tell you in their seminars that a high age low hour generator is garbage. A 3 year old gen with 600 hours is in better condition than one 8 years old with 200 hours. Been to multiple seminars all stating the same.
Also, as a note, around 14 and 15 Onan had some serious fuel pump diaphragm problems. I had the problem on a 2014 Sunseeker.
__________________
|
|
|
03-24-2023, 01:52 AM
|
#15
|
Senior Member
Brand: Still Looking
Model: Sunstar 29VE Winnebago
State: Texas
Posts: 4,332
THOR #13058
|
Quote:
Originally Posted by EA37TS
The Onan folks will tell you in their seminars that a high age low hour generator is garbage. A 3 year old gen with 600 hours is in better condition than one 8 years old with 200 hours. Been to multiple seminars all stating the same.
Also, as a note, around 14 and 15 Onan had some serious fuel pump diaphragm problems. I had the problem on a 2014 Sunseeker.
|
 I am going with what he is saying. I have not been to any of the seminars but I have stayed in a Holiday Inn Express.
When we added the EC-30 I had chance to talk with engineers from Onan. They state that owners of AGS system have a call in Support rate a lot lower than those without. Their theory or point is that if you own a AGS, in most cased the owners use it and when you use it you run the genny more than those without.
I try to get 100 hours a years but it is very hard to do. I run my genny for almost any reason I can think of. I never exercise it technically; because I use it for any excuse I can think of; so no need. I just serviced my genny two weeks ago.
For OP, I have seen error codes on my Onan 5500 and none of them required any service from Onan. Follow the advise you got earlier from The Ace on how to extract your codes. I could do the same thing but my EC-30 tracks and stores the last 10 error codes.
__________________
2019 Sunstar 29VE Sumo Springs; Safe T Plus; EC-30 AGS; Vmax 250ah AGM; T-Mobile Internet w/WiFi6; H/W Heater / Chassis Disconnect Switches; Southwire Surge Guard 44270 & 34951 w/Monitor 40301; Jet Flo Macerator; Alpine SPE500 Speakers; Visio M21D-H8R
|
|
|
03-26-2023, 08:56 PM
|
#16
|
Junior Member
Brand: Thor Motor Coach
Model: Thor Windsport
State: Florida
Posts: 26
THOR #28183
|
Thanks to all. Spoke to an Onan Service center here in Ocala, FL. He felt that all signs pointed to a faulty Fuel Pump. Picked one up and installed it. Generate cracked right up and ran for almost 1.0 hours non stop without any sign of trouble. Loaded it up with AC on high, External plug with air compressor filling up and not a single sign of trouble. I'm good with the fix!
Appreciate all inputs!!
NATO Rule: Don't worry about your enemies - it's your allies that will do you in.
__________________
|
|
|
03-26-2023, 09:02 PM
|
#17
|
Senior Member
Brand: Thor Motor Coach
Model: Freedom Traveller A27
State: North Carolina
Posts: 1,958
THOR #17765
|
Thanks for coming back to tell the forum about the fix
__________________
|
|
|
03-29-2023, 09:51 PM
|
#18
|
Junior Member
Brand: Thor Motor Coach
State: Georgia
Posts: 3
THOR #13503
|
Just maybe
IF. - your M H is low on its gas, the gen WILL NOT USE ALL OF YOUR GASOLINE. It will shut down.
Quote:
Originally Posted by AFLOGGIE
Good evening! My 2015 Thor Windsport 32n is equipped with a Onan 5500 GENSET. It has had all the right care but now it has decided to do shut off totally on its own without any command from me. There is no sign of overheating or other visible issues. We have been using the MH quite a bit and have run many gallons of gas through the tank. We live in central Florida and it has not been sitting in storage. I have put an additive in the tank to help keep the ethanol byproducts from building up in both the coach fuel injectors and the GENSET carb. It has just over 200 original hours on the meter.
Does any one have any suggestions as to why it is acting up? Looking forward to see what suggestions are out there.
Thanks,
AFLOGGIE
|
__________________
|
|
|
03-29-2023, 10:10 PM
|
#19
|
Senior Member
Brand: Still Looking
Model: Sunstar 29VE Winnebago
State: Texas
Posts: 4,332
THOR #13058
|
Post #16 the OP describe the issue and fix.
faulty Fuel Pump
__________________
2019 Sunstar 29VE Sumo Springs; Safe T Plus; EC-30 AGS; Vmax 250ah AGM; T-Mobile Internet w/WiFi6; H/W Heater / Chassis Disconnect Switches; Southwire Surge Guard 44270 & 34951 w/Monitor 40301; Jet Flo Macerator; Alpine SPE500 Speakers; Visio M21D-H8R
|
|
|
 |