Hi Bob, I have aluminum ramps I’ve used to help extend the ramp and lessen the angle. But they’re just one more thing to carry. And especially when only a couple of degrees would make things easier. Mostly curious as to why it suddenly comes up with that error message when twice before it never had an issue letting me raise the front end only.
|
Did you start from a different slope? Maybe your level sensor got knocked out of alignment. I’d start with a reset and then set zero point when on a known good level ground. The manuals I downloaded from Thor had the instructions; I think reset is holding the enter and retract together.
To set the Zero Point, first run a manual
leveling sequence to get the coach to the desired level point. Then activate the Zero Point configuration
mode. This mode is enabled by performing the following sequence:
1. Turn panel off.
2. Press the FRONT button (Fig. 1G) five times.
3. Press the REAR button (Fig. 1J) five times.
4. At this point, an alarm will sound and the LCD display will read "**ZERO POINT CALIBRATION** ENTER
to Set, POWER to Exit."
5. Press ENTER (Fig. 1C) to set the Zero Point.
6. Screen will then display "PLEASE WAIT."
7. Alarm will sound and the screen will display "ZERO POINT SUCCESSFUL."
8. LCD will display "configuring air feature".
9. Control will then turn off.