Unhappy Generator Problem, I think

Hi

I have a 2014 ACE 30.1 with the onboard generator. We are long term camping at a KOA in Monterrey Bay, CA and happy we are here. We use the 30AMP shore line with an inline surge suppressor and everything was working well. A few days ago the area had a power black out. Naturally everything went dark in the RV, although it was morning and sun was up. We wanted to use the microwave and I tried to start-up the generator. (I usually exercise the generator once a month routinely.) After a few cranks, the generator started, loped for a few seconds and then ran steady. When it switched to provide electricity (heard by the microwave beeping and refrigerator light go on), the generator shut off completely. I restarted the generator several times with the same result; shuts off completely. I checked the generator, had sufficient oil and the air filter was clean and there was no error indicator lights.

Luckily the power did come back on later in the morning. I was speaking with the head of maintenance about the issue. He said that actually they didn't have a black out, only a brown out. There was apparently about 60 VAC at the outlets. He suggested that if the generator has a line voltage sensor, this might cause the generator to shut down.

Is this true or should I be looking a different problem????

Robert
(owner of serenity, the RV)

__________________
rzeiler is offline   Reply With Quote
Old 06-17-2018, 12:32 AM   #2
Senior Member
 
Oneilkeys's Avatar
 
Brand: Still Looking
Model: Travato
State: Florida
Posts: 2,475
THOR #1765
Have you tried disconnecting from shore power, turning off all appliances and then starting the generator to see if it is now working correctly? You may not
be able to run the A/C and the microwave at the same time, if the generator is also charging the batteries. If the generator shuts down when you turn the A/C on, there will be a flashing code on the generator that may give you a clue to what is going wrong. If it just shuts down with nothing on, you still will get the code.
__________________
Oneilkeys is offline   Reply With Quote
Old 06-17-2018, 02:05 AM   #3
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,133
THOR #7035
The 60 VAC should have no effect on the generator. The Automatic Transfer Switch always gives preference to the generator so as soon as it sees proper voltage coming from the generator, it will switch to generator power even if you have full voltage from shore power.

You may have a fuel issue, maybe a fuel pump.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 06-20-2018, 04:38 PM   #4
Junior Member
 
Brand: Thor Motor Coach
State: California
Posts: 14
THOR #8117
Thanks, but the generator is fueled by propane. Thus no fuel pump.
Also, remember the generator started and ran until it started producing electricity (evidenced by the microwave beeping), but then shut off.
__________________
rzeiler is offline   Reply With Quote
Old 06-20-2018, 05:02 PM   #5
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,850
THOR #11130
I've never trusted anything to always function as designed...even the auto-transfer switch. I always disconnect from shore power before using generator.
__________________
Now an SOB
Traded Thor for Melbourne Prestige 24NP
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
Blondie passed in 2020 at 5 to Leukemia
The Gritz Carlton is offline   Reply With Quote
Old 06-20-2018, 05:04 PM   #6
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,850
THOR #11130
You might wanna check the spark plugs. How long since they were replaced? They will sometimes fire but under load they fail.
__________________
Now an SOB
Traded Thor for Melbourne Prestige 24NP
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
Blondie passed in 2020 at 5 to Leukemia
The Gritz Carlton is offline   Reply With Quote
Old 06-23-2018, 12:17 PM   #7
Senior Member
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Virginia
Posts: 315
THOR #7607
Propane? That's a new one on me. Anyway my genny stoped suddenly. It would start and run but die as soon as you took your finger off the start button. I wound up taking it to an Cummins-Onan service center. Turns out the genny has a 2 year or 2000 hour warranty, which saved me $1400 to repair it. They said the brushes arced and ruined the stator.
__________________
ComputerChips
ComputerChips is offline   Reply With Quote
Old 06-24-2018, 09:12 PM   #8
lug
Member
 
Brand: Thor Motor Coach
Model: ACE 32.1
State: Michigan
Posts: 85
THOR #11442
What's your propane level reading at the tank gage? Too low of a liquid volume creates a much lower vapor pressure resulting in fuel starvation for the generator. The stove, fridge, and heater may still function normal.
__________________
lug is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 03:58 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2