No power to outlets

The power suddenly went out to the outlets on the passenger side of my 2016 Thor Axis. Everywhere else power is good. Checked the fuses that says “right side” and “left side” to make sure, both were fine. Been plugged into shore power for weeks. Still plugged in.

Thoughts or suggestions appreciated 🤗

Thanks…

Dan

__________________
weatherbear is offline   Reply With Quote
Old 07-16-2021, 09:16 PM   #2
Senior Member
 
Brand: Thor Motor Coach
Model: Axis 24.1
State: Connecticut
Posts: 1,790
THOR #20289
You said you lost power to the left side "outlets". Were these 12V fixtures or 110V lamps plugged into outlets?

David
__________________
DavidEM is online now   Reply With Quote
Old 07-16-2021, 09:17 PM   #3
Senior Member
 
Brand: Thor Motor Coach
Model: '17-Vegas 24.1
State: California
Posts: 2,225
THOR #13362
Huh…
My box has two breakers for the outlets:
- GFI Outlets
- Non GFI Outlets

So in my rig they’re not categorized by right & left, just GFI & non-GFI.

Are you sure that the GFI outlet line works?
If not, it may be the breaker that’s integrated into the GFI outlet in the bathroom.
__________________
'17 Vegas 24.1
Fallbrook, CA
taylorbob1 is offline   Reply With Quote
Old 07-16-2021, 09:18 PM   #4
Junior Member
 
Brand: Thor Motor Coach
State: Utah
Posts: 23
THOR #17308
Quote:
Originally Posted by DavidEM View Post
You said you lost power to the left side "outlets". Were these 12V fixtures or 110V lamps plugged into outlets?

David
Just my usual stuff, coffee machine, blender, no power even to phone charger.
__________________
weatherbear is offline   Reply With Quote
Old 07-16-2021, 09:31 PM   #5
Senior Member
 
waynetaylor55's Avatar
 
Brand: Thor Motor Coach
Model: Four Winds 28A
State: California
Posts: 431
THOR #21941
Sounds like the GFCI circuit. Check the breaker (not fuse) and the GFCI outlet that has the trip button on it.
__________________
Wayne & Elissa
2021 THOR Four Winds 28A
Fallbrook, CA

Watchdog hardwired EMS, Alignment, Roadmaster front sway bar, vent covers, Dew Gutter
waynetaylor55 is offline   Reply With Quote
Old 07-16-2021, 10:07 PM   #6
Senior Member
 
Popfla's Avatar
 
Brand: Still Looking
Model: S.O.B.
State: Florida
Posts: 684
THOR #14543
Has to be the GFCI outlet. It looks like the one below. Buttons are for TEST and RESET. The buttons may be red and black. Usually found in the bathroom.
Attached Thumbnails
Click image for larger version

Name:	gfci.jpg
Views:	22
Size:	68.9 KB
ID:	32094  
__________________
Ed
Some Other Brand w/2020 Jeep Gladiator Toad
Living The Dream in "God's Waiting Room"
Popfla is offline   Reply With Quote
Old 07-16-2021, 10:15 PM   #7
Junior Member
 
Brand: Thor Motor Coach
State: Utah
Posts: 23
THOR #17308
Quote:
Originally Posted by Popfla View Post
Has to be the GFCI outlet. It looks like the one below. Buttons are for TEST and RESET. The buttons may be red and black. Usually found in the bathroom.
None of the outlets not working has this feature. There are 2. Though one does have a sticker on it that says GFCI PROTECTED OUTLET. 🤔
__________________
weatherbear is offline   Reply With Quote
Old 07-16-2021, 11:15 PM   #8
Senior Member
 
Brand: Thor Motor Coach
Model: Axis 24.1
State: Connecticut
Posts: 1,790
THOR #20289
Quote:
Originally Posted by weatherbear View Post
None of the outlets not working has this feature. There are 2. Though one does have a sticker on it that says GFCI PROTECTED OUTLET. 🤔
So somewhere either an upstream outlet is GFCI protected or the panel breaker is GFCI protected. Keep looking.

David
__________________
DavidEM is online now   Reply With Quote
Old 07-17-2021, 12:33 AM   #9
Junior Member
 
Brand: Thor Motor Coach
State: Utah
Posts: 23
THOR #17308
Quote:
Originally Posted by DavidEM View Post
So somewhere either an upstream outlet is GFCI protected or the panel breaker is GFCI protected. Keep looking.

David
Found it…thanx! Back corner of bedroom. Not sure why it tripped but it did.

Dan
__________________
weatherbear is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 07:01 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2