Old 11-27-2022, 10:34 PM   #1
Junior Member
 
Brand: Thor Motor Coach
State: Connecticut
Posts: 1
THOR #28575
Onan RV QG 4000

Driving in rain, generator running, then stopped running and won’t restart. Cranks but won’t start. Have 3/4 tank of gas.

On the road and using generator to run oxygen concentrator. Need help fast or will have to go to hotel.

Thanks

__________________
PamD is offline   Reply With Quote
Old 11-28-2022, 12:33 AM   #2
Senior Member
 
Brand: Thor Motor Coach
Model: Windsport 27K
State: Kentucky
Posts: 881
THOR #2817
Perhaps driving the RV at high speed on dry roads will eliminate water that might be causing the problem.
__________________
Metalman is offline   Reply With Quote
Old 11-28-2022, 03:49 AM   #3
Senior Member
 
MJC62's Avatar
 
Brand: Thor Motor Coach
Model: A.C.E. 27.2
State: Indiana
Posts: 1,874
THOR #14698
If it cranks over but won't start, I don't think the circuit breakers either in the MH or the one on the genny itself would be the problem.
I would try to start the genny outside at unit itself. Prime it and see if you can hear the pump if not that may be the issue. Or do you have a heavy smell of fuel? Perhaps the genny is flooded.
__________________
2018 ACE 27.2
Toad 2019 Jeep Cherokee Trailhawk
Roadmaster Falcon All Terrain Towbar
Roadmaster Invisibrake
MJC62 is offline   Reply With Quote
Old 11-28-2022, 04:06 AM   #4
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,326
THOR #7035
Quote:
Originally Posted by PamD View Post
Driving in rain, generator running, then stopped running and won’t restart. Cranks but won’t start. Have 3/4 tank of gas.

On the road and using generator to run oxygen concentrator. Need help fast or will have to go to hotel.

Thanks
Sounds like you have all the obvious bases covered. Most likely something in the generator control or ignition circuitry has gotten wet and needs to dry out.

You didn't say what RV you have but for future reference the oxygen concentrator should be able to run off an inverter so you wouldn't need to run the generator.. In fact, if you have an RV with a residential fridge you may already have an inverter installed - it doesn't power all the 120 VAC outlets, but there should be one you can plug the concentrator in to.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 12-07-2022, 08:17 PM   #5
Member
 
k.maslowski@comcast.net's Avatar
 
Brand: Thor Motor Coach
Model: AXIS 25.2
State: Tennessee
Posts: 89
THOR #6051
Just possible that with the wet weather something in the ignition is shorting. If you look at the attached pix (rotate it right) you will see a black spot on the intake manifold after the carburetor. The connector on the red wire was shorting when it got wet and would not let the GEN start or would quit after running a bit. A zip tie took care of the problem.
Attached Thumbnails
Click image for larger version

Name:	ONAN Carb spot.jpg
Views:	45
Size:	202.0 KB
ID:	40304  
__________________
k.maslowski@comcast.net is offline   Reply With Quote
Old 12-07-2022, 08:57 PM   #6
Senior Member
 
Brand: Thor Motor Coach
Model: A.C.E. 29.2
State: Oklahoma
Posts: 191
THOR #2542
Quote:
Originally Posted by PamD View Post
Driving in rain, generator running, then stopped running and won’t restart. Cranks but won’t start. Have 3/4 tank of gas.

On the road and using generator to run oxygen concentrator. Need help fast or will have to go to hotel.

Thanks
Remember, fuel, air, spark. Pull the plug wire, crank the genny and check for spark. It's easy enough to check the air filter. It is possible your fuel pump has failed. Pull the fuel line from the carburetor and prime the generator. If fuel flow is minimal or non existent, replace the pump and filter as a unit.
__________________
Rick Norris
Norrirn is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.


Thor Motor Coach Forum - Crossroads RV Forum - Redwood RV Forum - Dutchmen Forum - Heartland RV Forum - Keystone RV Forum - Airstream Trailer Forum


All times are GMT. The time now is 09:39 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2