I’m having a problem with one of my 110 volt circuits on my 22B class C. This has happened both at a campground and while at home. I’ve done the following to to try to find the issue:

1) Camper is 30 Amp

2) I have three GFCI outlets on one circuit. These work correctly.

3) I have 6 non GFCI outlets on one circuit that do not work.

4) Using a multimeter I have 124 volts coming off of the breaker of the non GFCI outlets. I did this by using the hot lead on the black hot wire and ground on the white neutral wire.

5) All wire connections are good at the breaker panel.

6) I removed all 6 outlets to inspect their wiring. They all looks good. Nothing burnt and solid connections.

7) When testing the bad outlets with the multimeter I see the following for each:
Hot to Neutral is 95 volts
Hot to ground is 124 volts
Neutral to ground 24 volts (should be zero)

8) When testing the good outlets I see the following:
Hot to Neutral is 124 volts
Hot to ground is 124 volts
Neutral to ground is zero volts

9) I’ve inspected what wiring visible and don’t see anything wrong.

10) I ensured to have nothing plugged into the outlets when testing them.

11) I do not have an inverter.

12) There is only one power feed from the transfer switch to the breaker panel.

13) Problem exists when on either shore or generator power

14) I don’t have any outlets in any storage bays and none of the six are GFCI. The six outlets are for the following locations:
Bedroom TV, Bedroom wall, Nightstand, Refrigerator, Booth table and front TV cabinet

__________________
2018 Thor Four Winds 22B
Abnmarine is offline   Reply With Quote
Old 12-21-2021, 11:32 PM   #2
Senior Member
 
Brand: Thor Motor Coach
Model: Citation
State: Texas
Posts: 920
THOR #8139
Greetings and Welcome

Have you found any junction boxes?
We have 1 screwed to the floor in the bedroom under the drawers.
Another 2 under a false floor under the sink.

Let us know.
__________________
abjbrtd is offline   Reply With Quote
Old 12-21-2021, 11:37 PM   #3
Junior Member
 
Brand: Thor Motor Coach
State: Florida
Posts: 2
THOR #24908
Thank you.

So far I have not found any. My breaker panel is under my bed and the wiring runs along the floor and wall with a carpeted cover over it. I will try to look some more.
__________________
2018 Thor Four Winds 22B
Abnmarine is offline   Reply With Quote
Old 12-21-2021, 11:44 PM   #4
Senior Member
 
waynetaylor55's Avatar
 
Brand: Thor Motor Coach
Model: Four Winds 28A
State: California
Posts: 431
THOR #21941
If you can figure out what order they are wired in, then you could disconnect each section, starting from the farthest away, and check voltages. You might find the culprit link. Probably a smashed wire somewhere.
__________________
Wayne & Elissa
2021 THOR Four Winds 28A
Fallbrook, CA

Watchdog hardwired EMS, Alignment, Roadmaster front sway bar, vent covers, Dew Gutter
waynetaylor55 is offline   Reply With Quote
Old 12-21-2021, 11:44 PM   #5
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,384
THOR #7035
Sounds like a poor connection on the neutral line for that circuit.

Plug in a simple device like a fan into the last circuit on the string and turn it on (a light would work as well).

Measure ground to neutral with the load - it will probably be line voltage (120 VDC). This indicates the neutral line is not connected properly to the neutral buss in the power center. Now you just have to find out why.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 12-21-2021, 11:50 PM   #6
Senior Member
 
Brand: Thor Motor Coach
Model: Citation
State: Texas
Posts: 920
THOR #8139
That's where ours is, the junction box in the bedroom is in the slide.

FYI: label the draws when you take them out, I didn't when insulating the outside wall, still trying to get the draws in the right order
__________________
abjbrtd is offline   Reply With Quote
Old 12-21-2021, 11:51 PM   #7
Senior Member
 
Brand: DRV
Model: 44' Santa Fe
State: Montana
Posts: 392
THOR #2053
Missing neutral is correct. Since all 6 outlets are affected, it is somewhere between, or at, the panel and the first outlet in the line. Look for either a j-box or a poor connection at the outlet. But it is a neutral problem.

Bill=retired EE with 45 yrs experience
__________________
If you are afraid to speak the truth out of fear of what others may think, it says a lot about who you are and what you will settle for.
Porkchop is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.


Thor Motor Coach Forum - Crossroads RV Forum - Redwood RV Forum - Dutchmen Forum - Heartland RV Forum - Keystone RV Forum - Airstream Trailer Forum


All times are GMT. The time now is 10:23 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2