Quote:
Originally Posted by CHS
First let me update my last post. I already have a double pole breaker (sorry for the confusion. My mistake.
So would it be advisable to change the breakers to be 30 amp (double pole)
I'm just concerned the 50 amp is too high, but then while in garage, it is only used to keep the refrigerator and/or the converter running. I guess the 30 amp main breaker and the 15 amp ones in the RV panel would cover those items.
|
My opinion here.
If you are only going to use the outlet for the RV from here on out. If it would comfort you better, make you more at ease. Then change out the outlet as needed, drop out the one leg not needed for 30A (disconnected & capped off at each end), and put in a 30A breaker. Save the components for if you want to switch back to the traditional 50 amp set up. The wire used for the 50A is no problem for the 30A it will be carrying. Going the other way, 30A to 50A is another story.
I believe Bob is saying it will be okay and work for you the way you are doing it, plus your own deduction of the RV breakers in line for the just in case.
When I made my RV parking spot, w/carport, I ran capability to upgrade to 50 amp from 30 (the extra leg there & breaker slot, inside the conduit, etc) so if I ever traded up to an RV that needs it.