Question Propane pressure drop

Experience request for propane plumbing.....!

Our 2007 Cougar 276RLS is experiencing a large propane pressure drop at all appliances under high demand (of the furnace). Furnace has been checked out at a good rv repair business, regulator has been replaced, lines are free of kinks. There are no noticable leaks in the system. Static pressure is around 15”, but drops to 2-4 on demand.

Next thought is that debris has gathered in steel or copper supply lines. Any experience out there on blowing the supply lines out and accessible screen locations, if any.

Maybe disconnect distribution at regulator outlet and connect compressor at stove supply, then blow out at 30-40 psi....?

__________________
PeterW is offline   Reply With Quote
Old 06-17-2020, 05:54 PM   #2
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
Since that's a closed system: I don't think that debris in the lines is your problem.
(This is a stoooopid question... but I have to ask... )

Have you checked for leaks at all of the connections?
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 06-17-2020, 07:24 PM   #3
Senior Member
 
Brand: Thor Motor Coach
Model: Hurricane 31S
State: Texas
Posts: 4,180
THOR #6411
Quote:
Originally Posted by PeterW View Post
Experience request for propane plumbing.....!

Our 2007 Cougar 276RLS is experiencing a large propane pressure drop at all appliances under high demand (of the furnace). Furnace has been checked out at a good rv repair business, regulator has been replaced, lines are free of kinks. There are no noticable leaks in the system. Static pressure is around 15”, but drops to 2-4 on demand.

Next thought is that debris has gathered in steel or copper supply lines. Any experience out there on blowing the supply lines out and accessible screen locations, if any.

Maybe disconnect distribution at regulator outlet and connect compressor at stove supply, then blow out at 30-40 psi....?
I would replace the single stage pressure regulator with a two stage and make sure the excessive-flow valve is reset and not sticking (if you have one). If you drive with the propane off and then suddenly open the tank valve, that can cause the excessive-flow valve to limit flow. To clear, turn the tank valve off. Bleed the propane system down. Next just crack the valve open and let it sit slightly open for an minute slowly pressuring the propane system. If you listen carefully you can hear a slight click when opening the valve and another as the system pressurizes. The first click it the valve closing limiting flow. The second click is the valve opening fully.
__________________
Jim & Roy Davis
2016 Hurricane 31S
1961 Rampside in tow
Beau388 is offline   Reply With Quote
Old 06-18-2020, 12:58 AM   #4
Junior Member
 
Brand: Keystone
State: British Columbia
Posts: 6
THOR #18665
No leaks in the system. Lines are still charged hours after last use.

No excess flow valve in the system. When appliances turn off, system comes right back to 15 lb
__________________
PeterW is offline   Reply With Quote
Old 06-21-2020, 03:51 AM   #5
Junior Member
 
Brand: Keystone
State: British Columbia
Posts: 6
THOR #18665
.....I mean 15 inches! New regulator is two stage.
__________________
PeterW is offline   Reply With Quote
Old 06-21-2020, 05:36 AM   #6
Senior Member
 
Travelin' Texans's Avatar
 
Brand: Redwood
Model: 36FB
State: Arizona
Posts: 1,766
THOR #3610
Quote:
Originally Posted by PeterW View Post
No leaks in the system. Lines are still charged hours after last use.

No excess flow valve in the system. When appliances turn off, system comes right back to 15 lb
Yes there is an excess flow valve built into every propane bottle, it's a safety feature to shut flow off in the event of an accident where the lines are damaged.
As mentioned open the valve slowly.
__________________
Fulltimed 10+ years
Sold '13 Thor Redwood 36 FB
Traded '13 GMC Denali DRW D/A
Replacement undetermined
Travelin' Texans is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.