30a shore power and generator same time

Question if hooked up to shore power and I want to test the generator will this cause any issues?

__________________
LAS CRUCES 2020 Thor Vegas 25.6
Lora & George. Golden Retriever & Multi-Gen Australian labradoodle & new ALD in March. Happy Campers!! E Biking, Hiking, Tennis, Scuba,Fishing,Cross Country Skiing, Snowshoeing. Retired H.S. Principal, Sr. IT Engineer, Life & Health Insurance Agent
"Today is a Gift and Why it is called the Present"
Scubawise is offline   Reply With Quote
Old 07-01-2021, 04:15 PM   #2
Axis/Vegas Enthusiast
 
Brand: Thor Motor Coach
Model: Axis 24.4
State: Michigan
Posts: 9,837
THOR #1150
It shouldn't. The generator has priority over the shorepower.

Of course if your transfer switch is mis-wired then it could cause an issue but when properly setup the generator has priority.
__________________
2022 Thor Axis 24.4
2021 Mach-E
blog - https://spareelectrons.wordpress.com/
JamieGeek is offline   Reply With Quote
Old 07-01-2021, 04:33 PM   #3
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
X 2...
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 07-01-2021, 04:43 PM   #4
Senior Member
 
Scubawise's Avatar
 
Brand: Thor Motor Coach
Model: Vegas 25.6
State: New Mexico
Posts: 5,100
THOR #20220
Thx generator showed fault ..but restarted and all works. Cleared fault
__________________
LAS CRUCES 2020 Thor Vegas 25.6
Lora & George. Golden Retriever & Multi-Gen Australian labradoodle & new ALD in March. Happy Campers!! E Biking, Hiking, Tennis, Scuba,Fishing,Cross Country Skiing, Snowshoeing. Retired H.S. Principal, Sr. IT Engineer, Life & Health Insurance Agent
"Today is a Gift and Why it is called the Present"
Scubawise is offline   Reply With Quote
Old 07-01-2021, 05:11 PM   #5
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
Quote:
Originally Posted by Scubawise View Post
Thx generator showed fault ..but restarted and all works. Cleared fault
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 07-01-2021, 06:55 PM   #6
Junior Member
 
Brand: Thor Motor Coach
State: Florida
Posts: 6
THOR #18052
Quote:
Originally Posted by JamieGeek View Post
It shouldn't. The generator has priority over the shorepower.

Of course if your transfer switch is mis-wired then it could cause an issue but when properly setup the generator has priority.
Funny this is brought up. My 2003 Hurricane, I tried to start my gennie yesterday while on shore power and all it did was make my generator buzz and wouldn’t turn over. Might have to do some checking.
__________________
UltraFinder is offline   Reply With Quote
Old 07-02-2021, 01:55 AM   #7
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
How old are your batteries?
__________________
Bob Denman is offline   Reply With Quote
Old 07-03-2021, 04:50 PM   #8
Junior Member
 
Brand: Thor Motor Coach
State: Florida
Posts: 6
THOR #18052
My batteries are 1.5 yrs. and always kept topped off. I’m assuming the generator uses the house batteries that is..
__________________
UltraFinder is offline   Reply With Quote
Old 07-03-2021, 05:13 PM   #9
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
Yes; it does.
__________________
Bob Denman is offline   Reply With Quote
Old 07-03-2021, 06:33 PM   #10
Senior Member
 
Brand: Thor Motor Coach
State: Missouri
Posts: 2,324
THOR #6903
It isn't required however I shut off my heavier electrical loads before starting the generator and then turn them back on

The transfer switch certainly (transfers) works under load but given the amount that fail I simply avoid that
__________________
lwmcguire is offline   Reply With Quote
Old 07-07-2021, 02:32 AM   #11
Senior Member
 
Mo_Mike's Avatar
 
Brand: Thor Motor Coach
Model: Vegas 25.2
State: Missouri
Posts: 1,038
THOR #4687
After having our transfer switch arc and melt wirenuts right from the factory, I have always tried to remove shore power before staring the generator. I know you "shouldnt" have to, however, an ounce of prevention...
__________________
2016 25.2 VEGAS with 2017 Jeep Wrangler AND Two Dogs; Norwegian Elkhound & Morkie (The RV is actually the Dog's)
Mo_Mike is offline   Reply With Quote
Old 07-07-2021, 02:57 AM   #12
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,132
THOR #7035
Quote:
Originally Posted by Mo_Mike View Post
After having our transfer switch arc and melt wirenuts right from the factory, I have always tried to remove shore power before staring the generator. I know you "shouldnt" have to, however, an ounce of prevention...
SP has no bearing on the "melt wirenuts" issue. It's simply poor workmanship on installation.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 07-07-2021, 03:43 AM   #13
Senior Member
 
Elite Washington's Avatar
 
Brand: Thor Motor Coach
State: Washington
Posts: 1,112
THOR #6433
We always start up the generator while on shore power when I know we will be using the air conditioning and power on the road. Get the generator going everything runs off of that so I don’t have to turn everything off when I unplug. Haven’t had any issues knock on wood.
__________________
2017 Freedom Elite 30fe 2013 Wrangler Unlimited toad.
Elite Washington is offline   Reply With Quote
Old 07-07-2021, 11:13 AM   #14
Senior Member
 
Bob Nodine's Avatar
 
Brand: Thor Motor Coach
Model: Quantum JM31
State: Tennessee
Posts: 688
THOR #21926
Everyone who owns an RV should once a year disconnect all the power and remove the cover on the transfer switch and the AC distribution panel and check the tightness of all the screws on the circuit breakers and relays. They tend to get loose with time and all the temperature fluctuations and bouncing around on the road. Once the connection deteriorates it starts to overheat at high current levels which causes a further increase in the resistance and it over heats even more and this effect continues until the contact fails and sometimes a fire can start. Many a transfer switch has failed because the contacts were loose.

As far as starting the generator with the shore power connected, a properly working transfer switch will disconnect the shore power relay before engaging the generator relay. There is a small circuit board inside the transfer switch that is connected to both the shore power side and the generator side and has small relays that control the large relays. The transfer switch defaults to the shore power side but will transfer the power source to the generator when it is present.

Where we get into trouble when starting the generator with the shore power on is if the air conditioners are running with the compressors on at the time of the transfer. When the shore power relay is disengaged while the compressor is on you can get arching at the relay contacts because you are disrupting the current to an inductive load. The inductance of the motor will try to keep the current flowing by increasing the voltage between the contacts thus causing the arc and burned contacts. Once you do this a few times you have a bad relay. I would make it a habit to turn off the shore power before starting the generator just to be on the safe side.
__________________
Bob
2022 Quantum JM31
2023 Colorado Z71
Bob Nodine is offline   Reply With Quote
Old 07-07-2021, 02:26 PM   #15
Senior Member
 
bevedfelker's Avatar
 
Brand: Thor Motor Coach
Model: 2015 Vegas 24.1
State: Pennsylvania
Posts: 1,468
THOR #2601
There are certainly lots of posts on the forum about failed transfer switches. Why temp fate by not turning off shore power?

All you'd have to do is be sure the AC is off, refrigerator off (AC), water heater off (AC) then start the generator.

I just think having shore power on and also running the generator is just asking for trouble.
__________________
Ed & Bev Felker
Retired USAF Col and retired Nurse
Traveling with Lily & Bella ('Teddy Bear' breed)
2015 Vegas 24.1 (E-350)
bevedfelker is offline   Reply With Quote
Old 07-07-2021, 03:00 PM   #16
I Think We're Lost!
 
Bob Denman's Avatar
 
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 22,195
THOR #8860
Quote:
Originally Posted by bevedfelker View Post
There are certainly lots of posts on the forum about failed transfer switches. Why temp fate by not turning off shore power?

All you'd have to do is be sure the AC is off, refrigerator off (AC), water heater off (AC) then start the generator.

I just think having shore power on and also running the generator is just asking for trouble.
https://www.thorforums.com/forums/at...1&d=1625670025
Attached Thumbnails
Click image for larger version

Name:	Floating Your Goat.jpg
Views:	74
Size:	149.2 KB
ID:	31902  
__________________
"What: me worry?"
Good Sam Member 843599689
Current coach: Tiffin Wayfarer 24 BW
Bob Denman is offline   Reply With Quote
Old 07-07-2021, 03:13 PM   #17
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,132
THOR #7035
Quote:
Originally Posted by bevedfelker View Post
There are certainly lots of posts on the forum about failed transfer switches. Why temp fate by not turning off shore power?

All you'd have to do is be sure the AC is off, refrigerator off (AC), water heater off (AC) then start the generator.

I just think having shore power on and also running the generator is just asking for trouble.
The posts about "failed transfer switches" are more about the connection wiring rather than the transfer switch itself failing. And when the transfer switch itself fails the mechanism is either:
The control board failed so it doesn't switch to generator when the generator is running, or
Contacts are burnt so no connection is made.

There are zero cases of the transfer switch connecting the generator and SP at the same time.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 07-07-2021, 05:26 PM   #18
Member
 
Brand: Thor Motor Coach
State: Florida
Posts: 59
THOR #24089
Thumbs up

Quote:
Originally Posted by Bob Nodine View Post
Everyone who owns an RV should once a year disconnect all the power and remove the cover on the transfer switch and the AC distribution panel and check the tightness of all the screws on the circuit breakers and relays. They tend to get loose with time and all the temperature fluctuations and bouncing around on the road. Once the connection deteriorates it starts to overheat at high current levels which causes a further increase in the resistance and it over heats even more and this effect continues until the contact fails and sometimes a fire can start. Many a transfer switch has failed because the contacts were loose.

As far as starting the generator with the shore power connected, a properly working transfer switch will disconnect the shore power relay before engaging the generator relay. There is a small circuit board inside the transfer switch that is connected to both the shore power side and the generator side and has small relays that control the large relays. The transfer switch defaults to the shore power side but will transfer the power source to the generator when it is present.

Where we get into trouble when starting the generator with the shore power on is if the air conditioners are running with the compressors on at the time of the transfer. When the shore power relay is disengaged while the compressor is on you can get arching at the relay contacts because you are disrupting the current to an inductive load. The inductance of the motor will try to keep the current flowing by increasing the voltage between the contacts thus causing the arc and burned contacts. Once you do this a few times you have a bad relay. I would make it a habit to turn off the shore power before starting the generator just to be on the safe side.
Good stuff...
__________________
Axis25.2 is offline   Reply With Quote
Old 07-07-2021, 06:50 PM   #19
Member
 
Brand: Thor Motor Coach
Model: Four Winds
State: Georgia
Posts: 78
THOR #8717
Quote:
Originally Posted by Bob Nodine View Post
Everyone who owns an RV should once a year disconnect all the power and remove the cover on the transfer switch and the AC distribution panel and check the tightness of all the screws on the circuit breakers and relays. They tend to get loose with time and all the temperature fluctuations and bouncing around on the road. Once the connection deteriorates it starts to overheat at high current levels which causes a further increase in the resistance and it over heats even more and this effect continues until the contact fails and sometimes a fire can start. Many a transfer switch has failed because the contacts were loose.

As far as starting the generator with the shore power connected, a properly working transfer switch will disconnect the shore power relay before engaging the generator relay. There is a small circuit board inside the transfer switch that is connected to both the shore power side and the generator side and has small relays that control the large relays. The transfer switch defaults to the shore power side but will transfer the power source to the generator when it is present.

Where we get into trouble when starting the generator with the shore power on is if the air conditioners are running with the compressors on at the time of the transfer. When the shore power relay is disengaged while the compressor is on you can get arching at the relay contacts because you are disrupting the current to an inductive load. The inductance of the motor will try to keep the current flowing by increasing the voltage between the contacts thus causing the arc and burned contacts. Once you do this a few times you have a bad relay. I would make it a habit to turn off the shore power before starting the generator just to be on the safe side.

Is there a typical place to look to find the transfer switch? My owner's manual does not provide that info.

Thanks, Dan
__________________
Danny boy is offline   Reply With Quote
Old 07-07-2021, 07:07 PM   #20
Senior Member
 
Bob Nodine's Avatar
 
Brand: Thor Motor Coach
Model: Quantum JM31
State: Tennessee
Posts: 688
THOR #21926
Quote:
Originally Posted by Danny boy View Post
Is there a typical place to look to find the transfer switch? My owner's manual does not provide that info.

Thanks, Dan
Dan,

It is usually as near as practical where the shore power cord enters the RV. I see you have a Four Winds which could mean it is under the bed or near a compartment where the shore power enters the coach. On our Quantum the transfer switch is accessible by removing a panel in the compartment near where the shore power connection is. In the attached photo you can see the transfer switch. The module in the upper left corner is the slide controller and the box at the bottom is just a junction box.
***********
I just noticed the photo somehow got rotated 90 degrees counterclockwise. In that case the slide controller is the module in the lower left corner.
Attached Thumbnails
Click image for larger version

Name:	20210705_080440.jpg
Views:	58
Size:	133.0 KB
ID:	31916  
__________________
Bob
2022 Quantum JM31
2023 Colorado Z71
Bob Nodine is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.




All times are GMT. The time now is 02:23 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO 3.6.0 PL2