Old 01-31-2019, 02:27 AM   #1
Senior Member
 
Brand: Thor Motor Coach
Model: Siesta
State: California
Posts: 112
THOR #3975
Question Trying to charge batteries @ home - GFI wall plate@ home triggered instantly

Hi, all.


We just got back from a 2 day overnite at a local beach. The battery indicator for the coach was 3/4. Before putting it into storage, I thought I would charge it a little at home. All I have at home is old-fashioned 110 volt.


I ran an ordinary 50 foot extension cord out to the RV, added an adapter from the 110 plug to the 30 amp plug needed by my Progressive Industries EMS box, plugged in the EMS box - it said all was good. Plugged the RV cable into the EMS box - and instantly lost all power to the EMS. Turned out the GFI wall socket had popped. Disconnected it all, reset GFI, then did it all again - same thing.


So - am I doing something inherently wrong? Could the EMS and GFI be incompatible with each other? Or the GFI junction box be wired wrong? I have used it for other ordinary electrical needs. I did not really want to plug into a non-GFI circuit without some more knowledgeable person saying "go for it - assuming your homeowners insurance is up to date..."


This is a 2016 Thor Siesta Class C with 2 x 12 volt batteries, and Prog Ind EMS-PT30C.


I don't really want to use the generator at home, or at the storage place... Just want to know if this SHOULD work. Longer term, I'll probably have some 30 amp service installed at home.


Thanks
Dan

__________________
lspotho is offline   Reply With Quote
Old 01-31-2019, 02:46 AM   #2
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,850
THOR #11130
Try another circuit at the home end of the extension cord that is not a GFI circuit.
__________________
Now an SOB
Traded Thor for Melbourne Prestige 24NP
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
Blondie passed in 2020 at 5 to Leukemia
The Gritz Carlton is offline   Reply With Quote
Old 01-31-2019, 03:35 AM   #3
Senior Member
 
Brand: Thor Motor Coach
Model: Siesta
State: California
Posts: 112
THOR #3975
Quote:
Originally Posted by The Gritz Carlton View Post
Try another circuit at the home end of the extension cord that is not a GFI circuit.

Well, sure - that's the obvious thing to do


Have to wait until I get a chance to bring it back from the storage place... probably a couple of days.


I'll post again after that.


Dan
__________________
lspotho is offline   Reply With Quote
Old 01-31-2019, 03:41 AM   #4
Site Team
 
16ACE27's Avatar
 
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 14,129
THOR #7035
Yep, use non-GFI. Your neutral and ground are probably bonded in your coach which your GFI does not like. Common issue.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
Old 01-31-2019, 11:49 AM   #5
Senior Member
 
Brand: Thor Motor Coach
Model: 37LS outlaw
State: New Jersey
Posts: 516
THOR #5248
Had same issue last year.
Found moisture in the outside 120v outlet on the coach.
Dried it out and then sealed it like Thor should have!
__________________
Trkyte@msn.com is offline   Reply With Quote
Old 01-31-2019, 12:49 PM   #6
Senior Member
 
Brand: Thor Motor Coach
State: Georgia
Posts: 2,585
THOR #4735
first, if you've already confirmed that your 'ems' is saying everything is fine, then BYPASS it and run directly to the outlet - chances are your ems doesn't like the GFCI outlet, or a combination of the RV's GFCI outlet and the shower power GFCI outlet - sometimes they don't play well together.

I've used GFCI circuits with no issues, but I also don't use any ems to get in the way.
__________________
TurnerFam is offline   Reply With Quote
Old 01-31-2019, 01:02 PM   #7
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,850
THOR #11130
Quote:
Originally Posted by lspotho View Post
Well, sure - that's the obvious thing to do


Have to wait until I get a chance to bring it back from the storage place... probably a couple of days.


I'll post again after that.


Dan

Why don't you list the things you know would be obvious to you...then we'll go from there. Just trying to help with suggestions from others that have experienced the same problem. Good luck with it!!
__________________
Now an SOB
Traded Thor for Melbourne Prestige 24NP
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
Blondie passed in 2020 at 5 to Leukemia
The Gritz Carlton is offline   Reply With Quote
Old 01-31-2019, 01:20 PM   #8
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
Quote:
Originally Posted by Tfryman View Post
Yep, use non-GFI. Your neutral and ground are probably bonded in your coach which your GFI does not like. Common issue.

Agree this can be an issue. I had this problem for a long time but ignored it since it was mostly an occasional inconvenience I could easily work around by plugging into non-GFI. Then I stayed at a nice RV campground where the 30-Amp were also GFI protected (at least the first time I was aware). That was a major inconvenience since other outlets (15 or 20) were GFI protected as well.

I figured other parks may start using 30A GFI breakers in future, so I finally fixed the problem. Now I can plug into any GFI without issues.

Just a heads up for those who may not be able to plug into GFI outlets at home.
__________________
Chance is offline   Reply With Quote
Old 01-31-2019, 02:00 PM   #9
Senior Member
 
The Gritz Carlton's Avatar
 
Brand: Thor Motor Coach
Model: THOR Chateua 35SF
State: Florida
Posts: 5,850
THOR #11130
Chance...what did you change to fix it?
__________________
Now an SOB
Traded Thor for Melbourne Prestige 24NP
2018 THOR Chateau 35SF
Two Labs, Bugsie & Blondie
Blondie passed in 2020 at 5 to Leukemia
The Gritz Carlton is offline   Reply With Quote
Old 01-31-2019, 02:11 PM   #10
Member
 
ddlonewolf50's Avatar
 
State: Arizona
Posts: 40
THOR #13531
Quote:
Originally Posted by Chance View Post
Agree this can be an issue. I had this problem for a long time but ignored it since it was mostly an occasional inconvenience I could easily work around by plugging into non-GFI. Then I stayed at a nice RV campground where the 30-Amp were also GFI protected (at least the first time I was aware). That was a major inconvenience since other outlets (15 or 20) were GFI protected as well.

I figured other parks may start using 30A GFI breakers in future, so I finally fixed the problem. Now I can plug into any GFI without issues.

Just a heads up for those who may not be able to plug into GFI outlets at home.
Hey Chance , where and how did you fix your GFI problem , I am very interested in this discussion now .
__________________
ddlonewolf50 is offline   Reply With Quote
Old 01-31-2019, 02:52 PM   #11
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
My neutral wiring was grounded at one location, and once I separated it, the problem went away.

I had not really thought about the problem fully until I consulted with a family member who’s an electrical engineer with lots of experience in this area.

As he explained it, even if there is a tiny bit of voltage at neutral at plug (talking about very low voltage due to normal voltage drop in house or campground wiring), then when I plugged in, that tiny bit of voltage would send a tiny amount of current down my neutral and back on ground wires.

Since the GFI compares current between neutral and power, it sees very low current on neutral, but not on line, so it tripped instantly even if I had nothing on inside camper.

If neutral and ground are connected at all, a GFI will likely trip instantly. It doesn’t take much because GFI trip at very low current differences, and since wires have very little resistance, even a “minor” voltage difference between ground and neutral will exceed the milliamps required.
__________________
Chance is offline   Reply With Quote
Old 01-31-2019, 04:25 PM   #12
Senior Member
 
Brand: Still Looking
State: Texas
Posts: 6,187
THOR #2121
P.S. — What I hadn’t considered before was that tripping the GFI didn’t involve the hot (120V) wire at all. I had previously checked by opening the main breaker, and also confirming that hot wire wasn’t grounded at all, but even then I kept tripping my GFI at home. It makes perfect sense now, but it took someone else to point it out. I kept looking for current flow from hot to ground, but that wasn’t the right place to look.
__________________
Chance is offline   Reply With Quote
Old 01-31-2019, 04:25 PM   #13
Senior Member
 
Brand: Thor Motor Coach
Model: Siesta
State: California
Posts: 112
THOR #3975
Quote:
Originally Posted by The Gritz Carlton View Post
Why don't you list the things you know would be obvious to you...then we'll go from there. Just trying to help with suggestions from others that have experienced the same problem. Good luck with it!!

Sorry - did not mean to make a snide comment, if that's the way it sounded... I really appreciate the responses here.



Anyway - the ONLY thing that was obvious to me was to try a non-GFI circuit - but I am not sure I have any... I guess the other obvious thing would be to skip the EMS. Or both. But those options sounded potentially dangerous - in that both the GFI and the EMS are supposed to prevent a more serious problem.


And I am completely unqualified to debug any other electrical problems.


But I will at least try bypassing the GFI, the EMS, or both...


Dan
__________________
lspotho is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off