Quote:
Originally Posted by schreinertms
Tried running both AC units while Onan 5500 gen running but only one AC unit would operate although both were on and set to a temp lower then the room temp. Is this normal as I was under the impression that a 5500 gen could run both AC units simultaneously.
|
You only have about 20 amps left over with the A/Cs running. Frig and converter take up most of the spare (both on L1). Turn on the microwave or the electric water heater and something will pop. You have 30 amps on L1 and 20 amps L2 usable. An EMS helps with this problem.