Xantrex ships their Pro and Freedom XI inverters with a GFCI installed in the face just below the monitor assembly. Also shipped are the block off plates and the communication cable. The Pro comes with a 15 amp pass through relay and the Freedom XI comes with a 30 amp pass through relay. If you feed a Freedom XI with #10 Romex through a 30 amp circuit breaker, you should use a supplemental breaker panel for the typical 15 amp branch circuits (#14 Romex). If you overtax the Xantrex inverters by tiring to exceed their rated output, you will get an E-05 hard shutdown fault. This fault will also disable the pass through relay. It is necessary to reset the inverter to use it again (remove all battery power for 10 seconds). On my coach tripping the tripping the 200 amp circuit breaker in the battery compartment won't do it. I had to remove the ground.