Done and Done!
I picked up a small load center box with two spaces and a couple of 15A breakers.
I took the output of the inverter and ran it straight to the load center. One breaker for the TVs & General outlets and the other for the fridge.
I hooked the fridge back up, but now through a breaker.
Then I ran some 14-2 wirecaped from where I pulled the run that used to go to the shorepower breaker. The other end connects to the "TVs and General Outlets" breaker in the new load center. I pulled the old 15A breaker in the shore power panel and put a blank back in..
The general outlets now work off of the inverter
I figured some 10-2 from the inverter to the new load center (about 3 ft) would be plenty for the two 15A breakers. Especially since the inverter has it's own breaker that would trip after 16A
Everything seems to work fine. I left the GFI Recepts on shore power. They are near the kitchen and the bathroom - where blenders and hair dryers might get plugged in.. That way, no one will come along and trip the inverter.
All sound okay?
Thanks for the help!
__________________
|