Quote:
Originally Posted by Judge
cut...
My panels are wired in parallel because the GoPower controller is a PWM controller. If I install an MPPT controller, I could wire them in series and that would reduce the current through the wiring to the Controller... but again the 10AWG should support 30A.
|
Remember, and I think you might have said this a long time back, if one panel goes out, they both go out. Pick up two more panels, if you have the room, and wire 2 sets of two in series and join them at a combiner box in parallel and run that to the controller.