Thread: Bathroom GFI
View Single Post
Old 11-13-2020, 06:36 PM   #5
DavidEM
Senior Member
 
Brand: Thor Motor Coach
Model: Axis 24.1
State: Connecticut
Posts: 1,794
THOR #20289
Quote:
Originally Posted by 16ACE27 View Post
No, ignore that post - it does not apply to your Outlaw with the onboard Onan generator.

The GFCI receptacle is just the beginning of a line of receptacles protected by the GFCI function. Since the GFCI receptacle has been replace numerous times you can probably safely say that is not the problem.
Since this only occurs when your generator is running it is probably a poor connection on one of the downstream receptacles. I'd disconnect the downstream receptacles from the GFCI receptacle to verify that, then start looking at/replacing the downstream receptacles.