Another way to think of it is that: The entire system will only consume as much as the smallest breaker/fuse. The smallest breaker/fuse will always be the first one to trip/blow.
Thus when a 30A RV is plugged into the dogbone into the 50A circuit it still can only draw 30A max (when the breaker in the RV will trip).
|