Quote:
Originally Posted by DavidEM
+1. I would never set the generator start level to less than 11.5V. Set the stop level at 13.5 or more since with the generator charging, the chart above is meaningless.
David
|
The chart above is a good reference for resting state voltage.
Under load the battery voltage can read 11.5V for a period of time but the batteries can still have well more than a 50% charge. The key is how long the voltage level is at a specific voltage.
Depending on which AGS the OP has, it should have a setting for not only the voltage to start the genny but how long the voltage remains at that level. My AGS has those settings as well and I base the AGS start for how long it stays at that voltage. I don't have access to my coach but if recall I'm set to 11.4V for 1 minute. Haven't had any issues and batteries still going strong.