There are certainly lots of posts on the forum about failed transfer switches. Why temp fate by not turning off shore power?
All you'd have to do is be sure the AC is off, refrigerator off (AC), water heater off (AC) then start the generator.
I just think having shore power on and also running the generator is just asking for trouble.
|
The posts about "failed transfer switches" are more about the connection wiring rather than the transfer switch itself failing. And when the transfer switch itself fails the mechanism is either:
The control board failed so it doesn't switch to generator when the generator is running, or
Contacts are burnt so no connection is made.
There are zero cases of the transfer switch connecting the generator and SP at the same time.