It trips on either A/C right? They should be on separate breakers and run from separate sides of the split 240 VAC lines.

In any case you probably need to unplug from SP and break out the Ohmmeter and start testing neutral to ground connections on the offending circuits. There should be no continuity from neutral to ground anywhere in the MH except on the output of the generator.

I would also quiz your battery installers. Did they have the most junior guy in the shop do this "simple" job and accidentally short + to ground? Did they do anything else in conjunction with the battery replacement where they may have driven a screw through a hidden wire?

When you figure this out please come back and let us know what you found to help out the next guy with a similar problem.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad - Selling
2020 Chevy Colorado Z71 Trail Runner Toad
2024 Chevrolet Trax 2RS - Soon 2B TOAD
16ACE27 is offline   Reply With Quote
 
» Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by Thor Industries or any of its affiliates. This is an independent, unofficial site.


Thor Motor Coach Forum - Crossroads RV Forum - Redwood RV Forum - Dutchmen Forum - Heartland RV Forum - Keystone RV Forum - Airstream Trailer Forum


All times are GMT. The time now is 05:59 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.