Quote:
Originally Posted by CountryFolk19
Thanks for getting me on the hunt.. ATS or gen breaker
I'll try testing that top breaker on the gen first. I really don't want to replace the ATS
Thanks everyone for the help
|
You can make your measurements for 120 VAC IN on each leg from the generator and verify both legs are being transferred to the load side by making measurements inside the ATS. Should be much easier to reach than the breakers on the generator.