I made all the changes some time ago posted by Ford Truck Guy plus a few more and our A/C performance is now acceptable all summer long.
1. Vent collars were too long into the vents, shorten the collar for better air flow
2. Vents were NOT sealed between the HVAC duct and collar, sealed vents so cold air does not leak into the attic space
3. The foam separator in the condenser had had fallen out, sealed with foil duct tape
4. The front cap had virtually no insulation (it had fallen down) climbed in front cap area of our 38FL and added insulation and secured it so it would not fall down (made a big difference in Front Living Room area)
5. Added ceiling registers (according to A/C manufacturer Redwood should have installed a minimum of 5 Registers per A/C unit (we only had 7 registers total, now we have 12 total, much better Air Flow / AC performance)
6. Added 2 additional returns on each unit and unblocked return area restrictions for better air flow / AC performance.
Rob, do you still have the drawings that you made of your modifications? It was your write up that helped me fix my AC flow in my last Redwood....