I have 5 year old CSW1012 Inverter. Never had an issue until today. I noticed that I am getting a E03 Error code which per manual it says the unit has sensed an overload or short circuit so it shut itself down after about 10 seconds.
However, I don't have any thing plugged into the Output? So there is no draw. My unit does not have hardwired to output. I have male receptacle plug I can simply unplug so nothing goes to my downstream inverter power supplied circuits.
I checked and I was getting 12.5vdc input to my CSW1012 Inverter.
When I try to push reset button it will not. It acts as if I have a ground fault.
What am I missing or anything else to try?
Context:
While I am just noticing this today, this issue is cause by a Memorial day weekend flat tire. The tire was banging and bent the inside compartment wall where this inverter was mounted. The impact was severe enough to jar the inverter off two of the mounting screws, but it otherwise was intact. The generator was running the entire time of changing out the flat; so I never noticed until today.
I have read some threads about a hard reset, but my manual does not say anything about hard resets? Trying not to wait until next week to call Magnum Technologies.
However, I don't have any thing plugged into the Output? So there is no draw. My unit does not have hardwired to output. I have male receptacle plug I can simply unplug so nothing goes to my downstream inverter power supplied circuits.
I checked and I was getting 12.5vdc input to my CSW1012 Inverter.
When I try to push reset button it will not. It acts as if I have a ground fault.
What am I missing or anything else to try?
Context:
While I am just noticing this today, this issue is cause by a Memorial day weekend flat tire. The tire was banging and bent the inside compartment wall where this inverter was mounted. The impact was severe enough to jar the inverter off two of the mounting screws, but it otherwise was intact. The generator was running the entire time of changing out the flat; so I never noticed until today.
I have read some threads about a hard reset, but my manual does not say anything about hard resets? Trying not to wait until next week to call Magnum Technologies.