Quote:
Originally Posted by 16ACE27
2.3 AC Amps is not a lot but the real question is:
If the "RV AC master breaker is turned off" (assuming you are talking about the double pole AC breaker in your Power center that removes SP from the breaker panel), why are you drawing ANY amps?
It could be the pass though coil on the EMS. It could be the SP activating coil on the ATS (if it has one) or, at 2.3 amps, I would say both. But that seems like a lot of current for 2 constant duty actuating coils.
But otherwise, it's perfectly normal for a single, or even multiple loads to pull from one hot leg. Other loads will pull from the other hot leg.
|
I wasn’t clear. I have 50 amp coming in. The master AC breaker in the RV is turned off. I am trying to isolate the “open neutral” to isolate the problem to the watchdog or the inverter. A little more research has shown that my charger only uses line one and since it’s the only thing running so those readings make sense. It ran all morning without issue, I have just turned on the main RV AC panel breaker but I’m not running anything to draw power. If it still doesn’t error I’ll start trying one breaker at a time with draw to see if I can find the problem.