Originally Posted by gmc
Time to get out the voltmeter... does require removing electrical covers and exposing potentially live wires - if you aren't comfortable working with electricity - then don't...
Before that - does the generator provide 110 to the coach?
If so - suspects would be shore power supply, power cord, connector to coach, surge suppressor (if present), and transfer switch.
If the generator doesn't provide power either - then start at the transfer switch - that's where the 2 sources come together.
At each point you should be able to measure voltage.. Assuming 50A rig - should read 110 from either hot to neutral, and 220 from hot to hot (if using a 50A to 30A adapter, hot to hot will read 0 volts - that is ok...)
If everything is fine up to the transfer switch - continue to the breaker panel.
Access will be the biggest issue - in my rig, most of that is under the bed.
|
Quote:
Originally Posted by beacoal
Greg here is what I have found out so far, yes the breakers have 110v to them and what I found out is that only the 2 airs, the converter and the inverter are on the breakers in the RV all the plugs including the GFI are somehow run through the inverter, I took apart the GFI and there is definitely no power the to it, I can see that a lot of the wire that would normally be hooked into the breakers are wired together and put through the inverter, (apparently the previous owner did a lot of dry camping) do you think that it would be ok if I undo the wire nuts and just rehook them to the breakers, and yes the genny is working fine but only powers the 4 breakers, Thanks Al
|
I don't see any issue moving wiring back to the breaker box...
Merging circuits together - while it functionally works - greatly limits the amount of power you can draw... Instead of 15a per branch circuit (up to the RV limit) - you have 15a for all when on shore power/generator - and of course limited by the inverter when dry.
The alternative is of course figuring out what is wrong with the inverter. Might be a simple breaker/reset on it - might be more.
(Something in between with one or two circuits on the inverter might make sense - all depends on how you intend to use it.)