06-13-2020, 10:11 PM
|
#21
|
Senior Member
Brand: DRV
Model: 38 RSB3
State: South Dakota
Posts: 2,066
THOR #1658
|
Quote:
Originally Posted by TurnerFam
because the nomenclature for 'regular household outlets' is a 15amp circuit, and which uses the 3-prong male end that we are all accustomed to seeing.
Campgrounds, RV parks, and many 'outside' and garage outlets at homes are 20amp outlets, since they may power tools and such.
While 'technically' a dedicated 20amp outlet, with 12/2 wire cable, and a 20amp breaker, will have a 'special' 3-prong male outlet, with one of the slots turned horizontal, most who install 20amp breakers and 12/2 wiring aren't trying to limit the usage to only tools or appliances with this special plug, but to allow simply MORE amperage to be used.
The only real difference between a 'normal' 15amp outlet and a 20amp outlet is the wire size and the breaker size - the outlet is typically exactly the same.
When the factories design and build these adapters, they can't use the term '20amp', since that is 'technically' relegated to only 'special' outlets, so they default to 15amps, which we all know and love.
You'll find though, when you arrive at most any rv park or campground, that the outlet's breaker is shown as a 20amp size, which gives you the greater amperage usage, but with the same male prong plug end.
So, yes, 'technically' it's a 15amp adapter, but for practical purposes it's able to handle the 20amp outlet you will be plugging it into.
|
I get that, what I was trying to say is, maybe these adapters are using a 14 gage (15amps) wire vs a 12 gage (20amps) wire. And that is why they say 15amps vs 20amps because of the gage of wire they used.
__________________
__________________
2016 DRV38RSB3
2015 Ram 3500 Regular Cab DRW CTD Asian trans 410 rear
|
|
|
06-13-2020, 10:13 PM
|
#22
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
remember, though, that the gauge wire is less important, if that, since it is such a SHORT run, full encased by the rubber exterior, and chances are you are not going to be pulling the full 20amps, in most any case, at least not for long. I imagine the factories know this, but don't use the term 20amp because that would infer the 'special' male plug, which it does not have.
__________________
__________________
|
|
|
06-13-2020, 10:16 PM
|
#23
|
Senior Member
Brand: DRV
Model: 38 RSB3
State: South Dakota
Posts: 2,066
THOR #1658
|
Quote:
Originally Posted by TurnerFam
and, interestingly enough, if you have two 13.5kw roof top a/c units, you CAN run both from just good 'ol regular 30amp RV service, no problem.
(having said that, there are many discussion here and on other forums of this 'disagreement', but many of us have done this quite often, in the hottest of months, when required - sure, you can't 'also' do everything else, like have the battery charger and electric water heater and microwave on at the same time, but with due diligence, it can work...)
|
I have read that people have wired in easy starts (I think that is what they are called) to their AC units. From what I read that it slowly kicks in the draw of an AC unit. As when it first turns on it draws it’s max load.
__________________
2016 DRV38RSB3
2015 Ram 3500 Regular Cab DRW CTD Asian trans 410 rear
|
|
|
06-13-2020, 10:20 PM
|
#24
|
Senior Member
Brand: DRV
Model: 38 RSB3
State: South Dakota
Posts: 2,066
THOR #1658
|
Quote:
Originally Posted by TurnerFam
remember, though, that the gauge wire is less important, if that, since it is such a SHORT run, full encased by the rubber exterior, and chances are you are not going to be pulling the full 20amps, in most any case, at least not for long. I imagine the factories know this, but don't use the term 20amp because that would infer the 'special' male plug, which it does not have.
|
Gotcha, I get the short run as longer runs need to be calculated. Thanks for your thoughts and explanation on that.
__________________
2016 DRV38RSB3
2015 Ram 3500 Regular Cab DRW CTD Asian trans 410 rear
|
|
|
06-13-2020, 10:23 PM
|
#25
|
Senior Member
Brand: Still Looking
State: Texas
Posts: 4,830
THOR #2121
|
Quote:
Originally Posted by TurnerFam
it works, yes, but only IF the smaller 15/20amp outlet is NOT a GFCI protected outlet...
I've done this many times, but generally the 15/20amp outlet is from another source, such as a nearby building, using an extension cord to reach it.
For some reason, the GFCI protected outlets, which are now common and normal in almost every campground and rv park, do not play well with these adapters, and they will not pass thru the power to the RV.
|
The reason is that the adapter shares the same common in the 50-Amp RV shore line (power cord) so the 30 Amp can go down one leg, and the 15/20 Amp can go down the other leg. However, when the (up to) 45~50 Amps returns combined down a single wire (the common), there’s no way to split the current “exactly” at the adapter between the 30A and 15/20A outlets so that the GFIC protected breaker doesn’t trip.
That’s all assuming that the 30A and 15/20A are all on same phase (an assumption made in posts above that’s not a given). In event that 30A and 15/20A are wired in pedestal to separate phases, the current imbalance coming back on the neutral will be even worse. Not that it makes a practical difference because the GFIC should trip either way when it senses an imbalance of a small fraction of one Amp.
Let me know if a numerical example would help clarify this.
__________________
|
|
|
06-13-2020, 10:24 PM
|
#26
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
and here's an interesting 'video' of various methods and electrical concerns and adapters, etc... real life stuff
__________________
|
|
|
06-13-2020, 10:34 PM
|
#27
|
Site Team
Brand: Thor Motor Coach
Model: ACE 27.1
State: Florida
Posts: 5,389
THOR #7035
|
Quote:
Originally Posted by Chance
The reason is that the adapter shares the same common in the 50-Amp RV shore line (power cord) so the 30 Amp can go down one leg, and the 15/20 Amp can go down the other leg. However, when the (up to) 45~50 Amps returns combined down a single wire (the common), there’s no way to split the current “exactly” at the adapter between the 30A and 15/20A outlets so that the GFIC protected breaker doesn’t trip.
That’s all assuming that the 30A and 15/20A are all on same phase (an assumption made in posts above that’s not a given). In event that 30A and 15/20A are wired in pedestal to separate phases, the current imbalance coming back on the neutral will be even worse. Not that it makes a practical difference because the GFIC should trip either way when it senses an imbalance of a small fraction of one Amp.
Let me know if a numerical example would help clarify this.
|
Why would they NOT be on the same phase on a 120 VAC only pedestal? If they had run 240 VAC to the pedestal they could have a 50 Amp plug.
__________________
Ted & Melinda
2016 ACE 27.1
2016 Chevy Sonic Toad
2020 Chevy Colorado Z71 Trail Runner Alternate Toad
|
|
|
06-13-2020, 10:36 PM
|
#28
|
Senior Member
Brand: DRV
Model: 38 RSB3
State: South Dakota
Posts: 2,066
THOR #1658
|
Quote:
Originally Posted by Chance
The reason is that the adapter shares the same common in the 50-Amp RV shore line (power cord) so the 30 Amp can go down one leg, and the 15/20 Amp can go down the other leg. However, when the (up to) 45~50 Amps returns combined down a single wire (the common), there’s no way to split the current “exactly” at the adapter between the 30A and 15/20A outlets so that the GFIC protected breaker doesn’t trip.
That’s all assuming that the 30A and 15/20A are all on same phase (an assumption made in posts above that’s not a given). In event that 30A and 15/20A are wired in pedestal to separate phases, the current imbalance coming back on the neutral will be even worse. Not that it makes a practical difference because the GFIC should trip either way when it senses an imbalance of a small fraction of one Amp.
Let me know if a numerical example would help clarify this.
|
What are the odds that the CG has a regular plug on a GFI breaker? As I know with homes that people are using GFI breakers in the panel vs at the receptacle.
__________________
2016 DRV38RSB3
2015 Ram 3500 Regular Cab DRW CTD Asian trans 410 rear
|
|
|
06-13-2020, 10:39 PM
|
#29
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
none
as they want the 'camper' to be able to reset it
__________________
|
|
|
06-13-2020, 10:43 PM
|
#30
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
Quote:
Originally Posted by 16ACE27
Why would they NOT be on the same phase on a 120 VAC only pedestal? If they had run 240 VAC to the pedestal they could have a 50 Amp plug.
|
Valid point, but also there's the possibility that several sites, all on the same Main breaker, are on opposing phases(hot leg 1, versus hot leg 2) from the 240v supply. Sites 1, 3, 5 are on the RED hot leg, and 2, 4, and 6 are on the other BLACK hot leg, more-or-less helping to 'balance' the load.
In reality, though, if the main breaker for the set of RV sites is a 200amp size, say, it would take over 200amps of usage between all the 1, 3, and 5 sites to trip the main breaker if none of the other sites were being utilized, but 30amps x 3 sites is only 90amps, so it's not really 'probable' that it's any potential problem.
__________________
|
|
|
06-13-2020, 11:30 PM
|
#31
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,278
THOR #15553
|
Quote:
Originally Posted by rynosback
Why would it not work? If it is providing you the addition leg over the 30 amps. I’m not an electrician but I understand basic fundamentals.
|
There is much more to electricity than your basic knowledge of it. Especially when it comes to GFI circuits and shared neutrals. GFI for simplicity is a mini computer.
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
06-14-2020, 12:11 AM
|
#32
|
Senior Member
Brand: Still Looking
State: Texas
Posts: 4,830
THOR #2121
|
When I said it’s not a “given”, it means it is not physically necessary and therefore we can’t assume it so. It may have been cheaper to wire that way (even if it doesn’t meet code — I’m not sure on that — people can take shortcuts to save money), but who cares why it could happen. The possibility is there. Assume nothing until confirmed. Regardless, it doesn’t matter either way because once L1 and L2 current is combined coming out of 50-Amp motorhome into a single neutral, the adaptor can not split it so precisely that the GFI protected circuit will receive exactly the same current in and out, and will trip.
For what it’s worth, I’ve stayed at one campground where even the 30-Amp service was GFI protected. That would further complicate matters using this adapter. That particular campground also had 50-A service so adapter wouldn’t have been required in the first place.
__________________
|
|
|
06-14-2020, 03:11 AM
|
#33
|
Senior Member
Brand: DRV
Model: 38 RSB3
State: South Dakota
Posts: 2,066
THOR #1658
|
Quote:
Originally Posted by cavie
There is much more to electricity than your basic knowledge of it. Especially when it comes to GFI circuits and shared neutrals. GFI for simplicity is a mini computer.
|
I would agree, that is why I said I understand the basic fundamentals. Thanks.
__________________
2016 DRV38RSB3
2015 Ram 3500 Regular Cab DRW CTD Asian trans 410 rear
|
|
|
06-14-2020, 05:18 AM
|
#34
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,278
THOR #15553
|
Quote:
Originally Posted by 16ACE27
Why would they NOT be on the same phase on a 120 VAC only pedestal? If they had run 240 VAC to the pedestal they could have a 50 Amp plug.
|
My camp has 2 pole 30's running to the PEDs. 240 volts to the buss bars. L1 and L2. A single 30 feeds the 30 amp outlet and a single 20 amp feeds the 20 amp GFI outlet. That's 240 inside the panel. No main breaker because there is less than 6 breakers. All per NEC. Electricity is not a DIY subject.
If they ran 50 amps they would have had to run much larger wire. $$$$$$$
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
06-14-2020, 01:43 PM
|
#35
|
I Think We're Lost!
Brand: Still Looking
Model: Tiffin Wayfarer 24 BW
State: New York
Posts: 17,840
THOR #8860
|
"CAv"
Between you and "Turner"; I'm thoroughly convinced to always call in the experts!
Thanks so much for all of the GREAT info!
__________________
|
|
|
06-14-2020, 01:57 PM
|
#36
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
Quote:
Originally Posted by cavie
My camp has 2 pole 30's running to the PEDs. 240 volts to the buss bars. L1 and L2. A single 30 feeds the 30 amp outlet and a single 20 amp feeds the 20 amp GFI outlet. That's 240 inside the panel. No main breaker because there is less than 6 breakers. All per NEC. Electricity is not a DIY subject.
If they ran 50 amps they would have had to run much larger wire. $$$$$$$
|
that certainly makes sense for a campground where the power pedestals are 30/20 setups... a double-pole 30amp 'main' breaker services each panel, and therefore only 10/3 wire cable is required, which is true: a LOT easier to deal with, and capable of handling this setup just fine.
Clarify what you mean by 'No main breaker', though. If there is a 30amp double-pole breaker set for EACH of these sites, in a Main Utility Panel on the property, I would guess, where then is the 'MAIN BREAKER' for all of these?
__________________
|
|
|
06-14-2020, 02:17 PM
|
#37
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,278
THOR #15553
|
Quote:
Originally Posted by TurnerFam
that certainly makes sense for a campground where the power pedestals are 30/20 setups... a double-pole 30amp 'main' breaker services each panel, and therefore only 10/3 wire cable is required, which is true: a LOT easier to deal with, and capable of handling this setup just fine.
Clarify what you mean by 'No main breaker', though. If there is a 30amp double-pole breaker set for EACH of these sites, in a Main Utility Panel on the property, I would guess, where then is the 'MAIN BREAKER' for all of these?
|
Yes, main breaker at the distribution panel. No main at the ped. Just 1 30 and 1 20. However, because of the distance and voltage drop the wire size should be a minimum of 1/0 at least just to get 30 amps. It is not. It is # 4 ALM and therefore I must use an autoformer on a 3 year old system. 116 volts with no load just don't cut it!
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
06-14-2020, 02:25 PM
|
#38
|
Thor Palazzo 33.3 diesel
Brand: Thor Motor Coach
Model: Palazzo 33.3 34'bunkhouse
State: Georgia
Posts: 2,448
THOR #4735
|
I see... well, that's pretty common at any campground or rv park pedestal - no 'Main' breaker at the pedestal since each circuit already has it's own breaker - a 30amp and 20amp, in your scenario.
The 'Main' breakers are at the campground's own Utility 'Main Panel', of which sometimes there are several, or many, depending on the size of the campground, number of sites, etc.
I don't see where, though, 116volts is any issue - seems like that's actually more 'normal' than not, most anywhere.
__________________
|
|
|
06-14-2020, 03:30 PM
|
#39
|
Senior Member
Brand: Keystone
Model: Sprinter
State: Florida
Posts: 1,278
THOR #15553
|
Quote:
Originally Posted by TurnerFam
I see... well, that's pretty common at any campground or rv park pedestal - no 'Main' breaker at the pedestal since each circuit already has it's own breaker - a 30amp and 20amp, in your scenario.
The 'Main' breakers are at the campground's own Utility 'Main Panel', of which sometimes there are several, or many, depending on the size of the campground, number of sites, etc.
I don't see where, though, 116volts is any issue - seems like that's actually more 'normal' than not, most anywhere.
|
127 is considered the normal delivery all over the US. 110 died with your grand dad. These days it is commonly know and 120/240.The problem with my 116, because of the undersized wire, quickly becomes 108 volts with the coffee pot. add the toaster and.......see where i'm going?
__________________
2011 Keystone Sprinter 323BHS. Retired Master Electrician. All Motor Homes are RV's. All RV's are not Motor Homes.
|
|
|
06-14-2020, 03:45 PM
|
#40
|
Senior Member
Brand: Still Looking
State: Texas
Posts: 4,830
THOR #2121
|
Yeah, middle of summer, A/Cs running all out, even lower voltage, higher current, followed by loss of power; leading to unhappy campers.
__________________
__________________
|
|
|
 |
|
Thread Tools |
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
|